ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
Do we need grounding?
by tortuga - 03/18/24 08:39 PM
Cordless Tools: The Obvious Question
by renosteinke - 03/14/24 08:05 PM
Test Post
by sabrown - 03/06/24 05:29 PM
Solar PV Wiring Errors
by renosteinke - 03/02/24 09:12 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
0 members (), 81 guests, and 12 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#30652 10/24/03 12:53 PM
Joined: Aug 2001
Posts: 545
A
aldav53 Offline OP
Member
In testing some switches in a home I was found a bad 4 way switch. But was picking up some weird voltages from the 3-ways feeding the 4-way, about 50 volts, but not enough current to light anything, just my little neon tester and Fluke meter. Don't know where this was coming from, maybe the wires were coiled up between the runs causing a coil-like (inductance effect) inducing some voltages. Any ideas?


The Golden Rule - "The man with the gold makes the rule"
#30653 10/24/03 02:09 PM
Joined: Aug 2001
Posts: 7,520
P
Member
It's most likely due to capacitive coupling.

When the light is switched on, one of the travelers is effectively disconnected by the 3-way switches at each end. Its proximity to the other conductors results in a small amount of capacitance.

Because a digital meter has a very high input impedance (typically 10 megohms), it takes only a small amount of capacitance to produce a substantial reading.

If you shunted the meter with some load, or used a conventional analog meter with a lower input imedance, then you would see a zero or much lower reading.

#30654 10/24/03 02:54 PM
Joined: Oct 2003
Posts: 289
:
Member
once at work i hat opened the breaker of a receptacle line for servicing. with the small neon screwdriver tester, i could see no difference between breaker on and breaker off. measuring with a tester with coil to montior the voltage then showed me the line was off.

Background: The cable was running in a troughing with several others. as both ends of the phase conductor were unconnected, the wire collected the field fromt he others...

#30655 10/24/03 03:20 PM
Joined: Oct 2000
Posts: 2,723
Likes: 1
Broom Pusher and
Member
As Paul has said, you are seeing the results of Capacitive Coupling (or some type of Reactive Coupling).

The Voltage reading on the DVM is from its high input Z (Impedance).
The Neon Lamp of the tester (probably a Proxy, non-contact type tester) is also seeing same thing.

Try reading with a Wiggy. The problem will go away.

p.s. With the Wiggy connected to the same circuit, try testing with the DVM; should have a very much lower Voltage reading now!

Scott35


Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!
#30656 10/24/03 04:31 PM
Joined: Aug 2001
Posts: 545
A
aldav53 Offline OP
Member
That makes sense, thanks..


The Golden Rule - "The man with the gold makes the rule"

Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5