ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Safety at heights?
by gfretwell - 04/23/24 03:03 PM
Old low volt E10 sockets - supplier or alternative
by gfretwell - 04/21/24 11:20 AM
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (Scott35), 523 guests, and 33 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Joined: Oct 2002
Posts: 830
S
Member
Anyone see anything wrong with putting bigger load in a generator panel than the generator is capable of carrying,(as long as the individual circuits are protected and the inter-locks are in place for the mains, and the panel is rated for the combined load, etc....etc.....)so that the individual loads can be turned on and off as needed??? For example....say you've got your well pump on and a few lights and receptacles, and you want to heat your water up, so you turn your lights or whatever off, and turn your water heater on... Am I missing something in the code.. Seems like this should be OK since, if the generator gets overloaded, it will shut down anyway??? Thanks again for the input..I want to make sure I got everything right..I've got a couple of these jobs coming up......... Steve

Joined: Oct 2000
Posts: 5,392
S
Member
In my experience, it's a good idea to have the customer participate in sizing the critical loads.

Trying to keep it simple , i usually ask that they add up this in wattage x 1.25%

However, when they realize the $$$ involved in higher KW genny's the issue of 'juggling always arises.

There are many undesized genny's that have an all inclusive auto-T switch , simply surviving on a crap shoot re; loads on @ time of transfere.

This, as opposed to the Gen-Tran 20216 or similar models that require manual intervention probably buys one little 'code' slack, yet makes 'juggling' loads a practical option.

Joined: Jul 2002
Posts: 8,443
Likes: 3
Member
Sparkynyc,
Do you guys, not have Maximum Demand Calculations, in the US?.
These give the fact,(called Diversity Factor),that not all of the loads will be drawing current at the same time.
We use these calcs, to size Mains and Sub-Mains, over here in New Zealand.
These Calcs, can also be applied to Gen-Sets
too, as they are the same as a Mains supply.
[Linked Image]

Joined: Jun 2001
Posts: 642
N
Member
The power companies use a derating factor from the calculated load of a building. This allows them to use smaller service wire than the calculated load would require if wired by the NEC. They know that electrical usage is not what the calculated load is. Different occupancies have different derating factors depending on simular loads served and thier usage history.
Check with the local utility and the AHJ before sizing the generator. Also find out from your customer what he really wants from the generator. You may be suprised how small the required generator will be. Of course if the customer has plans to add load later that should be addressed.
Good luck [Linked Image]


ed

Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5