ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Safety at heights?
by gfretwell - 04/23/24 03:03 PM
Old low volt E10 sockets - supplier or alternative
by gfretwell - 04/21/24 11:20 AM
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
0 members (), 516 guests, and 17 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#14690 09/29/02 08:29 AM
Joined: Sep 2002
Posts: 11
N
north Offline OP
Member
Is an elevator a continuos or intermitten load

Joined: May 2001
Posts: 717
G
Member
North,
I've had to do this and I believe they consider them intermittent.

It is regulated by ANSI 17.1.

Like any submittal, you have to ask the elevator contractor for his load ratings and include them in your own as an appliance.

If the contractor has not been selected yet, you can usually find one who will quote you load data. How tall, etc. is all they require. If the bldg is short enough you may have to 'guess' if they want to go hydraulic and you may find you'll have to adjust your calc after the elevator contractor is selected.

Most property owners use the same elevator company over and over.

Back to your question, the definition of intermittent is expected to last for 5 minutes or less, and most elevators never run for a continuous 5 minute period without stopping at a floor.

They design the equipment for continuous use however.

Joined: Oct 2000
Posts: 2,749
Member
See NEC Article 620 and the Annex D Example D9 Feeder Ampacity Determination for Generator Field Control, and Example D10 Feeder Ampacity Determination for Adjustable Speed Drive Control

See 620.13 and 620.61 in the 2002 NEC.

NEC Article 100 defines a continuous load as one that operates for 3 hours or more.

Duty, Continuous. Operation at a substantially constant load for an indefinitely long time.
Duty, Intermittent. Operation for alternate intervals of (1) load and no load; or (2) load and rest; or (3) load, no load, and rest.
Duty, Periodic. Intermittent operation in which the load conditions are regularly recurrent.
Duty, Short-Time. Operation at a substantially constant load for a short and definite, specified time.
Duty, Varying. Operation at loads, and for intervals of time, both of which may be subject to wide variation.


Joe Tedesco, NEC Consultant

Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5