#9489 04/30/02 08:10 PM
Joined: Aug 2001
Posts: 58
K
ken m Offline OP
Member
i have a question regarding a 3 & 4 way switch scenerio. box 'a' contains a 3 way with power and a light leads, box 'b' contains a 3 way with light and power, and the 4 way which is in the middle of course. question is...how can i wire the 2 light to operate properly without running a separate wire between them? i hope this makes sense. i'm taking over a wiring job that the origional contractor abandoned. also i thought i saw a reference here to a web site regarding various connection of 3 & 4 ways.
thx for any help! ken m

#9490 04/30/02 08:17 PM
Joined: May 2001
Posts: 36
C
Member
You may have 2-wire travelers...Is there a red wire in either box?

#9491 04/30/02 08:19 PM
Joined: Oct 2000
Posts: 5,392
S
Member
Ken.....try Here
or possibly Here
[Linked Image from darwinawards.com]

#9492 04/30/02 08:40 PM
Joined: Aug 2001
Posts: 335
S
Member
If you're saying you have 2 fixtures that need to be controlled from this system ... you need 4 conductor cable or a pipe system. Just run 4 conductors between the lights and you can put them "between" the switches. The conductors are 1 hot (or switched hot, depending where you sent the constant hot) 2 travelers and 1 neutral.
If you're stuck with 2 and 3 conductor cable you need to run the system in this order: 3 way-4 way-3 way light-light

#9493 04/30/02 11:47 PM
Joined: Oct 2001
Posts: 597
E
Member


Al Hildenbrand
#9494 05/02/02 06:27 PM
Joined: Mar 2002
Posts: 19
D
Member
Sparky,
Like the web sites I will show them to my classes.

Ken M.
Just for more info to keep in mind when you put four ways in. Depending on the manufacture of the four way some switch vertically and some switch horizontally.


Link Copied to Clipboard