Hello,
My costumer wants to power up some existing lights in a commerical building that has the service disconnected and service wires removed. Six foot away is another building with power in it, my plans are to run a short span of triplex from one building to the other and supply the lights with a single 20 amp circuit. Is this installation ok if I supply a service rated disconnect and bond the ground to the existing equipment?
|
|
|
|
Joined: Jul 2004
Posts: 9,932 Likes: 34
Member
|
Just remember to isolate the neutral in the second building and this is pretty straight forward. Bond the EGC to the building grounding system, connect your lighting circuit to the disconnect from your feeder.
Greg Fretwell
|
|
|
|
Joined: Jan 2005
Posts: 5,445 Likes: 3
Cat Servant Member
|
And, of course, connect to the ground rod for the second building.
|
|
|
|
Joined: Jun 2006
Posts: 613
Member
|
If you are using triplex to feed the second building you will not isolate the neutral and will be providing a new ground electrode connected to the new neutral. If you are housing livestock in the second building this is the only permissable way to do this unless a tingle voltage isolator is installed between the ground and neutral. If you are feeding the second building with ACWU, teck90, pipe and wire then you may run a bonding conductor to the second building panel and isolate the neutral from the ground.
|
|
|
|
Joined: Nov 2004
Posts: 14
OP
Member
|
Thanks people,
Renosteinke, does the single circuit EGC still connect to the ground rod? 250.32 (A) exception
|
|
|
|
Joined: Mar 2001
Posts: 345
Member
|
You must bond the Equipment Grounding Conductor of the branch circuit to the existing Grounding Electrode System. If you run quad-plex you can use either a multi wire branch circuit or if it's thirty amperes or more you can use it as a single phase feeder to supply the existing equipment. -- Tom Horne