636
18
The cold water ground thread brought up an old issue. An inspector asked me to insulate a conduit from HVAC duct. I'm assuming the idea is that a ground fault will be carried by the conduit, not the duct. I'm not quite following the reality that conduit is running to the furnace, which is multiple screwed to the duct. Since it's bonded there, what's the purpose of insulating it anywhere?
Dave
As there is no NEC section requiring this it seems your inspector just felt it was a good idea and you being the nice guy that you are you did it. Bob
Posts: 7,382 Likes: 7
I concur with Bob; did the AHJ reference a NEC Article?
I think he meant "separate." While not mentioned (afaik) in the NEC, I was taught that my conduit was not allowed to touch other utilities; where contact was unavoidable, a thick pad was used to separate the two.
I was taught that this was to prevent wear caused by isloation; we could rub holes in out pipes, but not anyone elses'.
The noise from pipe on duct would trigger a warranty callback.
Duct transmits sound better than a drummer in the basement.
Tesla
Tesla: Why would there be any noise? Conduit does not vibrate. There should be no vibration from the air handler/furnace either.
Not being a wise guy, but what do you base your comment on?
Reno: Yes, I also was 'taught' not to touch. I think Tiger has his furnace conduit strapped to the riser duct, which is common practice. I still don't see an NEC violation.