1 members (Scott35),
311
guests, and
12
robots. |
Key:
Admin,
Global Mod,
Mod
|
|
|
Joined: Jan 2006
Posts: 8
OP
Junior Member
|
Could push button connected to shunt trip coils be the disconnecting means for shore receptacles per NEC 555.17(B)? That's kind of remote contact to trip the circuit breaker for shore receptacles(500A).
------------------------------------------ NEC 555.17(B)Location. The disconnecting means shall be readily accessible, located not more than 762 mm (30 in.) from the receptacle it controls...
|
|
|
|
Joined: Jul 2004
Posts: 9,928 Likes: 34
Member
|
I believe the intent is that the user will be able to connect the shore tie cable without power being applied and then turn it on. How would you turn the shunt trip breaker back on ?
Greg Fretwell
|
|
|
|
Joined: Jul 2004
Posts: 9,928 Likes: 34
Member
|
I just went to several sources for the recomended procedures for checking shore ties and they all concur that you must turn off the power at the shore post and the breakers in the boat before you plug in the cable. Then you turn on the shore power, verify the polarity indicators in the boat read OK then turn on the boat breakers. You could not use a shunt trip for the post and follow this procedure without taking a long walk to a location you may not be aware of. That would encourage people to handle a hot cable in a wet environment. Bad idea.
Greg Fretwell
|
|
|
|
Joined: Oct 2004
Posts: 132
Member
|
What about a motor operated breaker with a remote open/close selctor switch, and indicator lights and/or meters to verify zero volts? What type of connectors are you using at 500A? Cam Lock?
Motor operated is expensive, but it might be cheaper than an extra 600A disconnect.
|
|
|
|
Joined: Jul 2004
Posts: 9,928 Likes: 34
Member
|
I agree that would meet the intent of the code.
Greg Fretwell
|
|
|
Posts: 806
Joined: October 2004
|
|
|
|
|