1 members (Scott35), 289 guests, and 11 robots.
F
Please give an example of where a non-fusible service disconnect can be used.
Thank you
[This message has been edited by Frank Cinker (edited 08-30-2006).]
Frank,
The only way you can do that is if you put the OCPD immediately adjacent thereto. 230.91
Don
As a "utility company" disconnect ahead of a meter socket it must be rated for service duty. They do not have OCP and are not the "service disconnect".
They are frequently used where a standard pull out meter socket is used for 480 V 3 phase, corner grounded, 200 amp or less on sewer lift stations. After the meter is the "service disconnect".
Bonding and grounding confusion with this kind of installation is extensive.
Alan--
Alan--