ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (Scott35), 381 guests, and 13 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Page 1 of 2 1 2
#99671 08/29/06 07:25 AM
Joined: Aug 2006
Posts: 4
C
Junior Member
Is the secondary feeder from a 75 kva xfrm protected from the primary breaker? I have a 100 amp 480 v breaker on the primary with a 200 amp 208 v secodary to a panel. Do I need a 200 amp main or can I use main lug and have the 100 amp breaker protect the 200 amp feeder?

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#99672 08/29/06 08:16 AM
Joined: May 2004
Posts: 162
C
Member
Proably not, and in this case I believe "NO" The OCPD installed per 450.3B protects the transformer proper, The secondary conductors are Tap conductors and must be protected in accordance with 240.21 (C)

Charlie

#99673 08/29/06 08:18 AM
Joined: May 2004
Posts: 162
C
Member
If this is a lighting and appliance BC panel board you must have not more than two mains, no MLO,

Charlie

#99674 08/29/06 03:49 PM
Joined: Jan 2004
Posts: 1,507
G
Member
The truth of the matter is if it's a single voltage secondary and a 3 phase Delta you can protect the secondary conductors with overcurrent protection on the primary. You could even use a MLO panel. Chances are tho, you have a secondary that would be more than one voltage and you need to protect the secondary conductors at their ampacity. You will be using the transformer tap rules in Article 240 for protecting these conductors. As for protecting the secondary of the transformer, you can protect it via the overcurrent protection on the primary sized @ 125% or limit the load on the secondary to the ampacity of the secondary with no more than 6 taps to overcurrent protection that does not exceed the ampacity of the secondary of the transformer.


George Little
#99675 08/29/06 04:24 PM
Joined: Jul 2004
Posts: 9,928
Likes: 34
G
Member
By "single voltage delta" I guess you mean corner ground


Greg Fretwell
#99676 08/29/06 07:10 PM
Joined: May 2004
Posts: 162
C
Member
Greorge
I'm not sure that you can go MLO if the panel qualifies as a lighting and appliance BC panel board .

Charlie

#99677 08/29/06 07:49 PM
Joined: Jan 2005
Posts: 155
D
Member
It is if my opinion that there is a lot of info missing such as if it's a 1ph 480-208v transformer with a 2w secondary(probably not though), a 480v 3ph delta-208vdelta (probably not either, but a educated "guess" would assume that it is a common 74kva 480v-208y/120 with a 3ph4w secondary which means that it would have both pri. and sec. OCPDs.
As a former application engineer to provide an answer based upon incomplete information as illustrated with this question is not wise.

#99678 08/30/06 07:21 AM
Joined: Nov 2000
Posts: 2,148
R
Member
Charlie,
Quote
I'm not sure that you can go MLO if the panel qualifies as a lighting and appliance BC panel board.
If you are working on one of those somewhat rare cases where the transformer primay OCPD is permitted to protect the secondary conductors, then you would have overcurren protection on the line side of the lighting and appliance branch cicuit panel board as required by 408.36(A).
Don


Don(resqcapt19)
#99679 08/30/06 05:34 PM
Joined: May 2004
Posts: 162
C
Member
Don I believe you are refering to 240.21(C) (5)???

I haven't given that application much thought but it is interesting


Charlie

#99680 08/30/06 06:26 PM
Joined: Oct 2000
Posts: 2,723
Likes: 1
Broom Pusher and
Member
carranoelectric,

I made a reply to this question at the Electrical Theory and Applications section.

The thread may be accessed using the following link:

Feeder Protection

or the "boring old, long version":
https://www.electrical-contractor.net/ubb/Forum7/HTML/000526.html

Scott35


Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!
Page 1 of 2 1 2

Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5