is 200.6 ment that you cannot re-identify a colored conductor(black,blue,red,ect...)smaller than #6 in pipe to a grounded conductor using white tape???
thanks, H20
|
|
|
|
Joined: Nov 2000
Posts: 2,148
Member
|
Don(resqcapt19)
|
|
|
|
Joined: May 2004
Posts: 162
Member
|
I agree with Don and it is done all the time
Charlie
|
|
|
|
Joined: Mar 2005
Posts: 240
OP
Member
|
|
|
|
|
Joined: Jan 2005
Posts: 5,445 Likes: 3
Cat Servant Member
|
I'm not at all sure that this wording in the code was deliberate. I agree, technically re-identifying a wire to make it white is not allowed.
Personally, I disagree with this rule. Argument aside, not a single supply house here carries #6 or #8 wire in any color but black. Ironically, sometimes the box dtores do!
Frankly, I am simply delighted when ANY attempt is made to properly identify conductors.
|
|
|
|
Joined: Jul 2006
Posts: 5
Junior Member
|
Amen to any attempt to identify the conductors. It seems to be too much trouble to go the extra foot to properly identify conductors when their purpose is not clearly demonstrated or seen.
|
|
|
|
Joined: Jul 2004
Posts: 9,928 Likes: 34
Member
|
I think the box stores carry colors because a homeowner is more likely to buy cut wire in these sizes. They also need the help to avoid confusion. Although I have seen pros who should know better get wires misidentified. Boom!
Greg Fretwell
|
|
|
|
Joined: Jul 2002
Posts: 717
Member
|
Simple personal opinion is it wouldn't be a bad idea to change the minimum size allowed to number 8. #10 and below is pretty common stuff on the shelves. The rule apears to have been written with big shops in mind. The ones that will carry lots of inventory. Time for an old quote from the past " Its the economy stupid"
|
|
|
|
Joined: May 2004
Posts: 162
Member
|
The rule apears to have been written with big shops in mind. The ones that will carry lots of inventory
I would be more inclined to believe it is the wire mfg that drive these types pf code issues, if all the mfg stopped making white insulation for 8AWG and 6AWG the languge would change.
Just a thought
Charlie
|
|
|
|
Joined: Jan 2004
Posts: 1,507
Member
|
You guys want some cheese with that whine?