ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Safety at heights?
by gfretwell - 04/23/24 03:03 PM
Old low volt E10 sockets - supplier or alternative
by gfretwell - 04/21/24 11:20 AM
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (Scott35), 235 guests, and 27 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Page 4 of 4 1 2 3 4
Joined: Jul 2004
Posts: 9,931
Likes: 34
G
Member
I'm glad I never had this fight. I really like them common trip, no matter where they go and the installers I worked with had the same opinion ... but they were generally the same guys who would "own" this installation after I left. I have OKed the #12 copper "tie" tho.


Greg Fretwell
Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Apr 2005
Posts: 116
X
Member
George,
I think that is where some people get confused. A "multiwire circuit" is, for example, a range outlet. It has to be fed with a multipole breaker, on different phases, which opens the two circuits simultaneously. These of course have to be side by side.
A "multiwire branch circuit" is more than one circuit, of different phases, sharing a neutral. For example, general purpose lighting and receptacle loads. These do not have to be side by side in the panel, and do not have to be opened simultaneously.

Joined: Jul 2004
Posts: 9,931
Likes: 34
G
Member
The code does address multiwire circuits that also have line to line loads and they are required to be common trip breakers. The real question is a MW that only has line to neutral loads.
I imagine all MW with require common trip some day if the code keeps going the way it does.
Eaton and SqD gotta eat too.


Greg Fretwell
Joined: Jan 2004
Posts: 1,507
G
Member
I was trying to make the point that if a multiwire branch circuit is to be disconnected simultaniously then it either needs to be a common trip breaker or multiple breakers that are side by side and tied together via a "Listed" handle tie. Unless of course you are in Florida.
(gfretwell territory)

Just jerking your chain Greg.

[This message has been edited by George Little (edited 09-20-2006).]


George Little
Joined: Jul 2004
Posts: 9,931
Likes: 34
G
Member
I may be a rebel but I think a 12 ga wire "formed" around the ends of the breaker handles is a better tie than that little pointy ended thing SqD sells. You sure don't lose it when you disturb the breakers.


Greg Fretwell
Joined: Jan 2004
Posts: 1,507
G
Member
Greg- I think a properly sized nail or a piece of #10 wire workes better than those sq D handle ties for sure and I agree with you. And you are also right- you are a rebel.