#99232 07/31/06 10:07 PM
Joined: Jul 2006
Posts: 5
S
sprkrob Offline OP
Junior Member
Today an inspector told me I cant put a flow and tamper switch on the same zone. My understanding is that they can be on same zone if they provide separate alarm and supervisory annunciation. This is a non addressable system. this is only thing on that zone and is programed waterflow/sup 1st floor. Am I correct???

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#99233 07/31/06 11:28 PM
Joined: Nov 2005
Posts: 827
Likes: 1
J
Member
How exactly were you planning to test for all those conditions on two wires of a non-addressable system?
Joe

#99234 08/01/06 06:50 PM
Joined: Jun 2002
Posts: 58
E
Member
They have to be separate or addressible: The tamper is a "trouble" or "supervisory" signal; the water flow is an "alarm" signal.

#99235 08/01/06 09:38 PM
Joined: Jul 2006
Posts: 5
S
sprkrob Offline OP
Junior Member
they are not separate but they do send different codes to central monitoring.
the zone is programed waterflow/supervisory.
flow switch sends alarm,tamper sends suprevision,trouble sends trouble.they are separate signals.there is also a separate ground fault LED. there is 2 resistors panel reads them.

#99236 08/04/06 11:01 AM
Joined: Mar 2001
Posts: 345
T
Member
sprkrob
Help me out here guy. I've done a fair amount of fire alarm work and I'm at a complete loss as to how you get separate supervisory and alarm indications on a single zone with non addressable equipment.
--
Tom Horne


Tom Horne

"This alternating current stuff is just a fad. It is much too dangerous for general use" Thomas Alva Edison
#99237 08/04/06 11:19 AM
Joined: Jul 2006
Posts: 23
R
Member
I've done a bit of FA myself and have never seen this one either. Please post back with the name and model of the panel.

#99238 08/04/06 06:41 PM
Joined: Jul 2006
Posts: 5
S
sprkrob Offline OP
Junior Member
OK
the panel reads 4.7K from EOL. You connect WF then 1.1k resistor then tamper then 3.6K then back through NEG. to panel. The panel reads the resistors. Pulls & smokes just have the 4.7 EOL on those zones. If the flow goes it reads 4.7 and goes to alarm. If tamper closes it reads 3.6 and supervision goes .You have to put 1.1 before tamper so panel can't read it. WF is NO, SS is NC. You program these zones to read it this way.

#99239 08/04/06 06:47 PM
Joined: Jul 2006
Posts: 5
S
sprkrob Offline OP
Junior Member
OH,
Trouble and supervisory are 2 different signals when programmed this way.

#99240 08/04/06 08:30 PM
Joined: Jan 2005
Posts: 316
L
Member
All I'm going to say is : Thank the powers to be for Addressable systems !!
Beats the hell out of those old hard wired systems.

#99241 08/04/06 09:13 PM
Joined: May 2002
Posts: 1,716
R
Member
Sprkrob is correct, I have done this in the past also.

I have also just used the tamper (with no reduced resistor) to show an open circuit and activate a trouble/supervisory signal.

I think the inspector is wrong and just not familiar with the installation.

Roger

[This message has been edited by Roger (edited 08-04-2006).]