0 members (), 373 guests, and 12 robots.
#99222 07/31/06 04:25 PM
rocha12 Offline OP
Article 314.16.C.2 states that a conduit body "shall be supported in a rigid and secure manner" yet 314.22.E says you can hang a condulet from an EMT pipe run. I don't believe that can be considered a "rigid and secure manner" Ideas welcome
#99223 07/31/06 04:33 PM
My Idea is your thinking about it to much. [Linked Image]
If you place EMT supports close to both sides of the conduit body it will be rigidly supported.
#99224 07/31/06 04:54 PM
rocha12 Offline OP
But the code allows up to 3' on either side of the condulet. It's not 12" any more
#99225 07/31/06 05:03 PM
Yes the code allows 36" but along with the EMT support requirements we must follow 314.16(C)(2).
It is a judgment call as to if 36" is close enough to meet 314.16(C)(2).
I am likely to support both sides of an LB within 12" on smaller EMT, on 4" EMT 36" will normally do fine.
Bob
#99226 07/31/06 05:09 PM
rocha12 Offline OP
I agree! How do you feel about drilling the condulet and mounting it to strut?
#99227 07/31/06 05:52 PM
Rocha12
I have seen that done, and I asked the magic question......'where does the mfg instructions say that is OK??'
Haven't seen an answer yet.
PS: Welcome to the forum; where are you located??
[This message has been edited by HotLine1 (edited 07-31-2006).]
#99228 07/31/06 05:55 PM
rocha12 Offline OP
I'm an electrical inspector at Lawrence Livermore Lab in Livermore CA.
I am also a contractor B & C10
#99229 07/31/06 06:07 PM
I have drilled a few conduit bodies in some instances where I wanted to add support. Mostly due to the pulling that I would be doing later.
I have also drilled drain holes in conduit bodies.
We are required to 'arrange to drain'.
IMO a small hole in conduit body can do this.
Is it it A-OK with the manufactures?
I doubt they say so publicly.
But come on we drill enclosures all the time for mounting or entering. [Linked Image]
JMO, Bob
#99230 08/01/06 07:50 AM
Bob:
I really know what you mean; been there, done that.
#99231 08/01/06 12:24 PM
I like the idea of rigidly mounting condolets too. I agree it is not necessary but it does give a lot more rigid installation than the one holers when a future user starts doing chin ups from the raceways.
