#99191 07/28/06 04:20 PM
Joined: Jan 2004
Posts: 1,507
G
Member
Can an electrician use a pop rivet to secure an equipment grounding conductor to the box if he terminates the wire in a ring connector?


George Little
Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#99192 07/28/06 05:03 PM
Joined: Jul 2006
Posts: 23
R
Member
Well he can but it would not meet NEC requirements unless it was listed for the purpose.

See 250.148 (C)

#99193 07/28/06 05:36 PM
Joined: Jan 2003
Posts: 4,391
I
Moderator
Rabbit, interestingly green ground screws are not listed for the purpose either.

George I am not sure, I see manufactures do it, of course many times they are very loose.


Bob Badger
Construction & Maintenance Electrician
Massachusetts
#99194 07/28/06 05:46 PM
Joined: Jul 2006
Posts: 23
R
Member
But 250.148 (C) does not say that the screw needs to be listed.

..........."by means of a grounding screw that shall be used for no other purpose or a listed grounding device."

#99195 07/28/06 08:48 PM
Joined: Jan 2005
Posts: 5,445
Likes: 2
Cat Servant
Member
Don't see why not... assuming the rivet is of the right size, and is properly installed.

I'm not going to focus on the rivet body as a 'conductor,' as it is my belief that a firm connection will result in current going directly from the wire, into the metal case... without any need for the rivet to conduct at all.

#99196 08/02/06 12:23 PM
Joined: Jul 2006
Posts: 33
E
Member
George,

Do you have insomnia and lie in bed at night and think these questions up? Actually it’s a good question. Who’s to say if a bolted connection is any better than a rivet if both are applied right? I have seen riveted grounding or bonding connections as you’ve described on UL listed equipment. That would indicate to me that it could be an approved application as long as the connection was made properly and to the manufactures’ specifications.

By the way gents, I am new to these boards and am an electrical inspector in the same area as George is. He is my mentor, very knowledgeable and a great guy. He has taught me a lot and has answered many questions when I’ve needed help. I’m looking forward to these discussions and have enjoyed lurking in the background.

Regards,

Tony T.

#99197 08/02/06 03:36 PM
Joined: Jan 2003
Posts: 4,391
I
Moderator
Welcome to the forum Tony T.

I agree with you, George comes up with some great questions that I have not seen asked before and most times do not have easy answers.


Bob


Bob Badger
Construction & Maintenance Electrician
Massachusetts
#99198 08/03/06 12:14 PM
Joined: Mar 2005
Posts: 399
A
Member
Rabbitgun got it right.
250.148 (C)
Alan--
For those that have the IAEI Analysis of Changes 2005 NEC page 82 has a related item about 250.8 and using a sheet metal screw to attach a lug to a panel = violation

[This message has been edited by Alan Nadon (edited 08-03-2006).]


Alan--
If it was easy, anyone could do it.