1 members (Scott35), 216 guests, and 11 robots.
#98959 06/28/06 08:47 PM
DO you need plugs behind bedroom doors?
My boss is killing me with this. I just hate the extra work for a plug I feel is useless.
When I asked him he said something like the 2002 code it wasn't required, but in the 2005 it is? Maybe it was the 1999 code it wasn't but 2002 it is.
Either way whats the verdict on this?
Shake n Bake
#98960 06/28/06 08:54 PM
Just to clarify.. I'm talking about the small walls that when the door opens it covers the whole wall.
Not talking larger walls. Just the walls that are over 2' but not any bigger than the door.
Shake n Bake
#98961 06/28/06 09:55 PM
210.52 does not offer any relief because of a door swing, If the "small wall" 2 feet wide it gets a receptacle.
Could the inspector miss it? Sure. But if he looks behind the door you will probably be buying some drywall.
#98962 06/28/06 10:21 PM
Greg:
Well said
#98963 06/29/06 05:17 AM
I agree with Greg as well.
I recommend you adjust your thinking. [Linked Image]
Your an electrician, your job is wiring to meet code.
That means code required items are never 'useless'.
#98964 06/29/06 12:16 PM
V
My boss wants recpticals behind the doors. His thinking is you will always have a place to plug the vacume cleaner into. Makes sense to me. Rod
#98965 06/29/06 02:17 PM
I normally put these 3' - 3 1/2' above floor. No point in having to bend over to plug in vacuum.
#98966 06/29/06 03:58 PM
I don't know how wide the doors are in your town, but the NEC requires residential outlets so that no point along the floor line of the wall is greater than 6 feet from a receptacle. Three 16 inch bays make 4 feet.
Using the following system, you will never have to place one behind the door: Start your measurements from each side of the rough frame openings; within 6 feet install the first receptacle, then space the rest, somewhat equally, so that there is never more than 12 feet between receptacles.
The measurement goes "as the mouse travels around the room". You even have to count that little 3 inch piece directly next to your door frame. Any entry door, fireplace, doorway, closet door openings or the like start the process all over again. But, windows (even floor to ceiling windows) count as wall space. This means the patio door that is half glass and half door can be a problem (the 6 foot measurement will have to start in the middle of the opening for one side). Same story for "pocket doors". The 9 foot wide, three section, door-window-door unit requires a floor box.
Those wall sections that are shorter than 2 feet between door openings are the only ones that escape this rule. Walls that are between 2 and 12 feet in length between doorways can get by with a single receptacle in the center.
You will never have to make the excuse: "Oh, that one is for the vacuum cleaner!" again.
By the way, this rule has been in the NEC for all of my career, which spans over 30 years.
Earl
#98967 06/29/06 04:16 PM
I don't see an exception for closets. Perhaps we need recepts inside of closets also.
One needs to read the code in a rational manner.
I would not require recpts in closets (most of my closets have them) and I would not require recepts where a normally open door would cover the entire wall section.
#98968 06/29/06 04:35 PM
George "closet" is not one of those rooms listed in 210.52(A) but I still think a receptacle is not a bad idea, particularly if there is a counter in there. That is where my wife plugs in her cell phone and palm chargers.
It is a design decision not a code one.
I suppose we could start the closet in a bedroom thing here too [Linked Image]
