The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Live Chat

Join in a Live Electrical Chat!
Live Electrical Chat
>> Enter/Register
 

  Sorry, your browser is not Java enabled, please visit our java support pages in Chatroom
Recent Posts
recall notice Cooper Lighting light reflector
by sparkyinak
Yesterday at 06:34 PM
450.3(C)
by Tesla
Yesterday at 04:07 PM
100AMP panel in 60 degree ambient what size wire?
by sidmuer
Yesterday at 09:25 AM
One Doorbell Button to 4 Doorbells/Chimes
by sparkyinak
05/21/12 11:37 PM
Housekeeping and Clean-up
by renosteinke
05/21/12 12:52 PM
New in the Gallery:
An old Amprobe model 550
Shout Box

Top Posters (30 Days)
gfretwell 27
HotLine1 27
sparkyinak 18
twh 15
renosteinke 14
Classified Ads:


Electrical-Classifieds.com

Who's Online
0 registered (), 96 Guests and 2 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#98801 - 06/07/06 07:16 PM Pancake box
George Little Offline
Member

Registered: 01/18/04
Posts: 1445
Loc: Michigan USA
Are the inspectors allowing 3" pancake boxes for mounting light fixtures? Remember the cu. in. fill for this size box is 4 cu. in.
_________________________
George Little

Top
#98802 - 06/08/06 07:57 AM Re: Pancake box
renosteinke Offline
Cat Servant
Member

Registered: 01/22/05
Posts: 4653
Loc: Blue Collar Country
Sure- and why not?

Indeed, they are often used for ceiling fans as well.

The only problem is wire fill... if the circuit continues on to another fixture, then wire fill is violated. There's only enough room (legally) for one set of wires.

Top
#98803 - 06/08/06 09:50 AM Re: Pancake box
Alan Nadon Offline
Member

Registered: 03/10/05
Posts: 398
Loc: Elkhart, IN. USA
Short answer NO
4 cu inches ( 65 cm cubed) allows for the end of a 14 / 2, no ground, nothing else.
Fixture canopys add space but, unless they are marked with the Cu. In. they should not be counted.
Almost anyplace that a pan box can be used an L shaped box, i.e. pan with a wiring compartment on one side, would do better.
I once asked an engineer at Raco why they kept making the 3" pans and he said, Because inspectors kept allowing them to pass inspection.
Alan--
_________________________
Alan--
If it was easy, anyone could do it.

Top
#98804 - 06/08/06 08:38 PM Re: Pancake box
BigB Offline
Member

Registered: 03/31/04
Posts: 570
Loc: Tucson, AZ USA
reno you must be thinking he said 4" pancake like I did at first.

Top
#98805 - 06/08/06 11:54 PM Re: Pancake box
Tesla Offline
Member

Registered: 06/16/04
Posts: 768
Loc: Sacramento, CA
Use listed #18 lighting whips in 3/8" Flex.

Problem gone....

You will need to have a junction box within 6 feet for the listed whip.

Alternately, for lighting only you can use the tap rules to run your own #18 even longer.

Look at NEC 2005 table 240.5

[This message has been edited by Tesla (edited 06-09-2006).]

[This message has been edited by Tesla (edited 06-18-2006).]
_________________________
Tesla

Top
#98806 - 06/09/06 05:56 PM Re: Pancake box
renosteinke Offline
Cat Servant
Member

Registered: 01/22/05
Posts: 4653
Loc: Blue Collar Country
Big B, I bet you're right. I'm not sure I've ever seen the smaller one!

Top
#98807 - 06/12/06 07:06 PM Re: Pancake box
Ryan_J Offline
Moderator

Registered: 08/19/03
Posts: 1355
Loc: West Jordan, Utah, USA
I let people use them if there is only one 14-2 in the box.
_________________________
Ryan Jackson,
Salt Lake City

Top
#98808 - 06/13/06 12:19 AM Re: Pancake box
gfretwell Offline

Member

Registered: 07/20/04
Posts: 7146
Loc: Estero,Fl,usa
Doesn't the fixture canopy add to the capacity?

 Quote:
410.10 Space for Conductors.
Canopies and outlet boxes taken together shall provide adequate space so that luminaire (fixture) conductors and their connecting devices can be properly installed.


If the luminaire had a flat base that effectively stopped the box fill at the face of the box I could see the concern but if this is a bell canopy there should be plenty of room, even for two sets of #12s.
_________________________
Greg Fretwell

Top
#98809 - 06/13/06 05:01 AM Re: Pancake box
George Little Offline
Member

Registered: 01/18/04
Posts: 1445
Loc: Michigan USA
410.10 makes no mention of using the canopy of a fixture as space for branch circuit conductors, only the fixture conductors and their connecting devices. The branch circuit conductors are poperly housed in the box. If it were a 4" pan box it would properly house a single 14/2 WG NM cable and the fixture wires could be housed in the canopy. A 3" pan box is quite clearly not suitable for 14/2 WG NM cable but most of us, like Ryan would accept it.

Typo's

[This message has been edited by George Little (edited 06-13-2006).]
_________________________
George Little

Top