Are the lugs and screws that are installed on pool & spa equipment by the factory suitable for bonding the equipment to the bonding grid? Do inspectors ask that the contractors replace these lugs and screws with ones made of stainless steel, brass or copper or other non-corrosive material?
George Little
Stay up to Code with the Latest NEC:
>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep
>> 2020 NEC & Related Reference & Study Guides
#98755 06/04/06 09:39 PM
Yes, and they shouldn't.
Larry Fine
Fine Electric Co.
fineelectricco.com
#98756 06/05/06 06:20 PM
George:
I have to agree with Larry
Yes, and why are they requested/required to be replaced??
#98757 06/05/06 09:15 PM
John & Larry- I agree with you guys and so does UL. Once you start altering a UL Listed equipment you are inviting problems. The equipment is Listed with the lugs on it and that's where we connect the Bond wire. But, we still have some inspectors out there that read the wording about brass, copper or stainless connections and they have the contractors changing them. I say they are wrong for doing so.
George Little
#98758 06/06/06 06:09 PM
George:
Perhaps it's time for a little CE or Seminar on Article 680??
Only mention of the SS, Brass of Cu lugs that I'm aware of regards bonding IG???
Maybe I missed something??