#98616 - 01/23/05 06:48 PM Can you paint the front of a receptacle?
Joe Tedesco Offline
Member
Registered: 10/07/00
Posts: 2749
Loc: Boston, Massachusetts USA
Question: Can you paint the front of a receptacle if you do not get any paint on the contacts?

Answer: No, receptacles are not evaluated with paint on the device.

Following is a quote from UL:

"A receptacle which has been painted other than authorized by the file procedure, for example, "Charlie home owner, etc., would no longer be UL Listed. The introduction of paint, especially on the face of the outlet could reduce spacing or form a tracking either line to line or line to ground."

In addition, to the potential hazards associated with reduced spacing or tracking, it is possible the paint itself could be conductive.

Courtesy: www.nema.org
_________________________
Joe Tedesco, NEC Consultant
Top
2017 / 2014 NEC & Related Books and Study Guides
#98617 - 01/24/05 09:02 AM Re: Can you paint the front of a receptacle?
gfretwell Offline


Member
Registered: 07/20/04
Posts: 9036
Loc: Estero,Fl,usa
The manufacturer's association says if you get paint on it you have to replace it, imagine that.
U/L said "receptacles are not evaluated with paint on the device" so they don't know.
_________________________
Greg Fretwell
Top
#98618 - 01/24/05 09:40 AM Re: Can you paint the front of a receptacle?
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
My own opinion is that this is a non issue.

I find nothing in the UL white book that says we can not paint a receptacle. I have not seen that info in the limited instructions that come with a receptacle.

I also think that this is entirely unenforceable which just makes it a joke.

IMHO there are more important things to worry about.

Bob
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#98619 - 01/24/05 10:29 AM Re: Can you paint the front of a receptacle?
Joe Tedesco Offline
Member
Registered: 10/07/00
Posts: 2749
Loc: Boston, Massachusetts USA
Take a look at the FAQ's and see the answers given around the country, one of the representatives from Texas is the Chairman of CMP 1 and the other from Massachusetts his alternate, Andre works for UL and Mike is a Midwest Code Guru.

I thought the message here would rattle a few cages, but how does the judge and jury see this issue:

Have fun!
http://www.nema.org/stds/fieldreps/
_________________________
Joe Tedesco, NEC Consultant
Top
#98620 - 01/24/05 01:07 PM Re: Can you paint the front of a receptacle?
George Offline
Member
Registered: 02/23/02
Posts: 375
Using that reasoning ...

You cannot paint conduit. Incidental drips are included in painting.

I wonder if they test recepts with the grounds up or down. That would settle that argument once and for all.
Top
#98621 - 01/24/05 01:57 PM Re: Can you paint the front of a receptacle?
cpal Offline
Member
Registered: 05/17/04
Posts: 162
Loc: Cohasset MA
Joe the link does not appear to offer FAQ at the NEMA site.

Are you certain the URL is correct??


Charlie
Top
#98622 - 01/24/05 04:33 PM Re: Can you paint the front of a receptacle?
Joe Tedesco Offline
Member
Registered: 10/07/00
Posts: 2749
Loc: Boston, Massachusetts USA
Charlie:

Look to the upper left of the page and find these links that will take you to the FAQ area.

Field Representative Program
Code Alerts
Field Representatives: Frequently Asked Questions
_________________________
Joe Tedesco, NEC Consultant
Top
#98623 - 01/24/05 05:46 PM Re: Can you paint the front of a receptacle?
cpal Offline
Member
Registered: 05/17/04
Posts: 162
Loc: Cohasset MA
Thanks Joe
Top
#98624 - 01/25/05 03:38 AM Re: Can you paint the front of a receptacle?
Joe Tedesco Offline
Member
Registered: 10/07/00
Posts: 2749
Loc: Boston, Massachusetts USA
Non issue?

_________________________
Joe Tedesco, NEC Consultant
Top
#98625 - 01/25/05 04:58 AM Re: Can you paint the front of a receptacle?
Roger Offline
Member
Registered: 05/18/02
Posts: 1716
Loc: N.C.
Tamper resistant.

Roger
Top
Page 1 of 2 1 2 >

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
1 registered (cableguy619), 64 Guests and 7 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals