200A service with 4/0 alum. cond. what size GEC is okay? i know that table 250.66 says #4 but im in an arguement with someone who says it's not required to be any larger than #6. also, there is no rebar ground and plastic water service. what do you say?
Stay up to Code with the Latest NEC:
>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep
>> 2020 NEC & Related Reference & Study Guides
#98541 05/31/06 10:43 PM
Bob Offline
250.66(A) says #6.
#98542 05/31/06 11:35 PM
A driven ground never needs more than #6 cu. Any other electrode, #4 cu.
Larry Fine
Fine Electric Co.