0 members (), 345 guests, and 27 robots.
#98434 02/20/05 08:45 PM
334.80 says type NM (romex) shall have conductors rated 90 degrees C
So...the romex used in the 80's had conductors rated 60 degrees C
So... in this kitchen remodel I'm doing (the one we already determined that I have to replace the type SE range line), can I use the old branch circuit romex feeding the kitchen, which has conductors rated 60 degrees C, bring them into a juction box and extend new 90 degree C romex to the new plug locations, dishwasher, micro, etc???
The panel is located in a plastered garage and it will be difficult to access.
Or would Mass Rule 3 apply here also?
shortcircuit
#98435 02/21/05 09:56 AM
I think you would be ok. I have done this many times and the only time it was ever questioned the inspector wanted to make sure the old wire did not connect directly to a light fixture.