I wrote a violation last week to a contractor who had installed a duplex receptacle on a wall and it had a nub in between the two blades of the receptacle that prevented one from pluging in anything but a special cap with a recess that would straddle the nub on the receptacle. For me this does not satisfy the code for a general purpose receptacle required by 210.52 NEC. He ended up installing a duplex receptacle with half of it with the nub and half of it without the nub. He then split wired the receptacle so he could control half of it with the home automation system and the other half would serve the wall space as a general receptacle. Was I wrong?
George Little
|
|
|
|
Joined: Feb 2005
Posts: 693
Member
|
George, that's a good question. Is there anything in the NEC that specifies the receptacle configuration?
I see 125v, 15- and 20-amp receptacles, but nothing that prohibits, say, a twist-lock. The nub is to reject the insertion of a non-dimmable load.
Larry Fine Fine Electric Co. fineelectricco.com
|
|
|
|
Joined: Feb 2005
Posts: 693
Member
|
oops
[This message has been edited by Larry Fine (edited 05-28-2006).]
Larry Fine Fine Electric Co. fineelectricco.com
|
|
|
|
Joined: Oct 2005
Posts: 141
Member
|
I'm not an inspector but agree with you. How can the receptacle satisfy the requirement of a general purpose receptacle when it is a special receptacle that will only take a certain cord?
|
|
|
|
Joined: Jul 2004
Posts: 625
Member
|
It seems to me that a dimmer-controlled receptacle (I'm making that leap that the receptacle is dimmer-controlled, because that is the purpose of those particular receptacles) does not meet the G.P. receptacle requirements of 210.52.
|
|
|
|
Joined: May 2003
Posts: 2,876
Member
|
Funny I brought up the same thing with someone doing the exactly same about the same time. Otherwise, it doesnt cover spacing for general use.
Mark Heller "Well - I oughta....." -Jackie Gleason
|
|
|
|
Joined: Feb 2005
Posts: 693
Member
|
Okay, I'll play devil's advocate here.
Where does the NEC specify that a required receptacle be only a straight-blade or "non-nubbed" type, or must or must not be of any particular configuration?
[This message has been edited by Larry Fine (edited 05-29-2006).]
Larry Fine Fine Electric Co. fineelectricco.com
|
|
|
|
Joined: Jan 2003
Posts: 4,391
Moderator
|
Okay, I'll play devil's advocate here. Cool, someone has to. Where does the NEC specify that a required receptacle be only a straight-blade or "non-nubbed" type, or must or must not be of any particular configuration? It does not, but it does require we use 15 or 20 amp 125 volt receptacles. While a locking receptacle can meet this I bet the 'special purpose' receptacle is rated less than 15 amps. Even if the receptacle is rated 15 or 20 amps I would also bet the circuit supplying it is not. I doubt the home automation equipment uses an 1800 watt or larger dimmer for a table lamp.
Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|
|
Joined: Feb 2005
Posts: 693
Member
|
Remember, Bob, standard dimmers are rated at only 600 watts, and do not require OC protection at this (5a) level.
Larry Fine Fine Electric Co. fineelectricco.com
|
|
|
|
Joined: Jan 2003
Posts: 4,391
Moderator
|
I agree Larry but there is no requirement for 15 or 20 amp lighting outlets. There is a requirement for a 15 or 20 amp receptacle circuit.
Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|