Is Romex wire forbiden by NEC to be used in commercial facilities? Which article?
Thanks,
Joe.-
|
|
|
|
Joined: Jun 2004
Posts: 1,273
Member
|
There is no absolute prohibition.
Romex is not permitted over soft lids: that shoots it down for most commercial -- but not all.
Many AHJ's will still not accept Romex -- but that's not in the national code. It's a local thing.
Tesla
|
|
|
|
Joined: Dec 2003
Posts: 751
Member
|
A soft lid, to me, is a comfy felt hat, instead of the construction hard hat. What is it to you? NM cable can be used in commercial work if the building construction is of types III, IV or V. Or, in more easily understood terms, where wood walls are allowed, so is Romex.
Earl
|
|
|
|
Joined: Jun 2003
Posts: 681
Member
|
NM cable is permitted in metallic type studs as well. You need to read 334.10 & 334.12.
NM cable itself is not prohibited from "occupancy" types, it has other location type uses/restrictions.
Pierre Belarge
|
|
|
|
Joined: Jul 2002
Posts: 717
Member
|
One non code word of caution. I've seen it used in resturants. I've also seen the insulation stripped clean off by rats in resturants. So if there is food handling in the commercial building, I would not use it myself, no matter the type of building construction.
|
|
|
|
Joined: Jun 2003
Posts: 681
Member
|
I am surprised we have not heard much lately about creatures eating away at NM cable.
I know that recently manufacturers of NM cable have been putting a chemical in the sheathing that deters creatures from chewing on the sheathing.
Pierre Belarge
|
|
|
|
Joined: Jul 2002
Posts: 717
Member
|
That is good to know. I wonder what chemical it is that they are putting in there.
|
|
|
|
Joined: Jun 2005
Posts: 821
Member
|
I didn't know about the chemical thing either. Good to know.
|
|
|
|
Joined: Jul 2004
Posts: 9,928 Likes: 34
Member
|
Don't taste any different to me Wouldn't that have to be on the MSDS?
Greg Fretwell
|
|
|
|
Joined: Jul 2002
Posts: 717
Member
|
Greg, you hit it right on the nose with the taste thing. I remember a big fat electrician named Tony who I worked with in 1978 wiring 7 Lakes in Ft. Myers. He slapped me on the back of the head when he saw me holding a short piece of wire in my mouth. In his day they put arsenic into wire to keep rats off of it. Thats what I call OJT.
|
|
|