ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
0 members (), 390 guests, and 14 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#98045 05/01/06 12:06 PM
Joined: Feb 2006
Posts: 18
R
rhpope Offline OP
Member
Is it legal to use a 4 conductor cord in place of 4 individual wires to run a circuit in EMT from the 3 phase distribution panel to a 3 phase air compressor? The cord has Red/Black/White/Green wires. At either end of the cord where the outer sheath is skinned back, can the white wire be wrapped with blue tape to indicate it is one of the hot leads instead of a neutral?

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#98046 05/01/06 12:33 PM
Joined: May 2002
Posts: 1,716
R
Member
I assume you are referring to a cord that would fall under article 400, and if that is correct, see 400.8(6).

Roger

#98047 05/05/06 08:08 AM
Joined: Sep 2003
Posts: 650
W
Member
Has anyone encountered cable that is listed both as a flexible cord (one of the cable types in table 400.4) and which is _also_ listed as a cable assembly suitable for fixed wiring (eg. type NM, TC or one of the others)?

-Jon

#98048 05/05/06 07:46 PM
Joined: Apr 2002
Posts: 7,381
Likes: 7
Member
Winnie:
Frankly, no. Last 'new' item I ran into is PVC coated MC cable. Can't say your cord doesn't exist, but haven't seen it.

RHpope:
400.8 (1) prohibits cord being used for permanent wiring. ('02 & '05)

Basically, if you're running EMT, why not THHN??? (Probably cheaper also)

John


John

Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5