#98002 04/24/06 11:56 AM
Joined: Jan 2004
Posts: 1,507
G
Member
Is there another place in the NEC or IRC that references the connector requirements when installing cables in conduit sleeves? I found 312.5(C) and I'm thinking there is another code reference that says you don't need a clamp inside the box to secure the cable to the enclousure.


George Little
Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#98003 04/24/06 12:27 PM
Joined: Jul 2004
Posts: 9,928
Likes: 34
G
Member
You sort of get there with 334.15(B),300.10 ex1 if only by omission.
If you are coming out of a box, exposed to some degree of physical damage it is normal to sleeve cables in EMT or RNC up to a safe height, where it gets secured upon exiting the raceway.


Greg Fretwell