When the instructions with the "Household Fire Alarm" panel tell the installer to ground the equipment by connecting To a water pipe
I would like to know:
<OL TYPE=1>
[*] Does this equipment require to be BONDED to the GES,
[*] Does this equipment simply need to be Electrically BONDED to the system - the EGC,
[*] Is a supplimental Bonding Conductor required - which is Bonded to the GES at an "Effective Point", due to this equipment containing a MODEM, or similar device,
[*] If the instructions are just being as basic as possible - removing any liability on the Manufacturer's end.
</OL>
Semi-loaded questions, but not for trouble-starting purposes.
Have seen many FACPs with the noted "Ground Lugs", yet they all did not contain equipment which would warrant a bond to the GES.
They all used "Kind-Of Universal" enclosures, which resulted in all having the Ground Lugs - but only one actually needed to have a bond to the GES - the one with the event dialer (since the POTS circuit was dedicated to the FACP. the line pair was run directly from the TELCO's "PET" - and it is bonded to the GES, so does it really need to be bonded again?).
Have seen similar stuff on Alarm System Panels (Intrusion Alarms, etc.), Building Automation System Panels, and Audio Equipment for use in Commercial / Industrial locations.
Scott35