d
Stay up to Code with the Latest NEC:
>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep
>> 2020 NEC & Related Reference & Study Guides
#97687 03/14/06 01:49 PM
Rabbit Offline OP
Sorry. Had a little trouble remembering my password at work. Anywy, is there a maximum distance a disconnect can be from an outdoor unit? Providing line of sight is maintained?
#97688 03/14/06 06:47 PM
Assuming you're referring to HVAC equipment (a condensor in particular), the disconnecting means according to article 440.14 says that it must be within sight of the unit and be readily accessible.
#97689 03/14/06 08:46 PM
Rabbit Offline OP
Yeah, thats what we think too. A friend had this question on a state exam and was given four multiple choice answers. I don't remember the specific answers but they were all footages. I can't find anything.
#97690 03/15/06 07:38 PM
See the definition of "In Sight From" in Article 100. It includes a distance of 50 feet.
#97691 03/16/06 07:02 PM
Rabbit Offline OP
That was it. Thanks!