#97478 02/21/06 11:52 AM
Joined: Aug 2001
Posts: 545
A
aldav53 Offline OP
Member
When running multiple circuits from a panel to a juction box then splitting circuits off from there. I only need one ground to the junc box (sized to the largest conductor) then tie the rest of the grounds to a ground bar or lug from there. I don't need indivdual grounds for each circuit, unless its a GFI circuit. Correct?


The Golden Rule - "The man with the gold makes the rule"
Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#97479 02/21/06 01:17 PM
Joined: Jul 2004
Posts: 9,928
Likes: 34
G
Member
Are you talking about equipment grounding conductors? Then yes, you just need one, sized to the largest O/C device.
The GFCI question confused me.


Greg Fretwell
#97480 02/21/06 02:24 PM
Joined: Nov 2000
Posts: 2,148
R
Member
I don't know what a "ground" is. Are you asking about the grounded conductor or the equipment grounding conductor?
Don


Don(resqcapt19)
#97481 02/21/06 04:14 PM
Joined: Aug 2001
Posts: 545
A
aldav53 Offline OP
Member
Yes, equipment ground conductor. Not the neutral.


The Golden Rule - "The man with the gold makes the rule"
#97482 02/22/06 02:43 PM
Joined: Mar 2001
Posts: 345
T
Member
Quote
Yes, equipment ground conductor. Not the neutral.
Then I'd say your original question gets a yes answer but I don't see how the circuit being GFCI protected has any bearing on the question of the Equipment Grounding Conductor. Since the EGC does not pass through the sensing mechanism of the GFCI having only the one would have no effect on the GFCIs performance.
--
Tom

"This alternating current stuff is just a fad. It is much too dangerous for general use." Thomas Alva Edison

[This message has been edited by tdhorne (edited 02-22-2006).]


Tom Horne

"This alternating current stuff is just a fad. It is much too dangerous for general use" Thomas Alva Edison
#97483 02/22/06 09:01 PM
Joined: Aug 2001
Posts: 545
A
aldav53 Offline OP
Member
Your right, I probably don't need a separate ground for the GFI either, (neutral yes) but not ground. I'll just run the 3 - #8's for the spa heat pump to the pool equipment area junction box and branch off for the pool pump and GFI ground from there. I could run the motor frame bond wire there also. Where do they usually run the motor bond wire?


The Golden Rule - "The man with the gold makes the rule"
#97484 02/22/06 10:52 PM
Joined: Jul 2004
Posts: 9,928
Likes: 34
G
Member
The only place you need an insulated, unspliced EGC is to a pool underwater light J box.


Greg Fretwell
#97485 02/24/06 02:25 AM
Joined: Mar 2005
Posts: 240
Member
"then tie the rest of the grounds
to a "ground bar or lug"

how about some big blue wire nuts?
i have seen grounding conductors split bolted b-4, is it legal or smart for that matter to put several under a split bolt?

h20

#97486 02/24/06 08:53 AM
Joined: Feb 2003
Posts: 31
S
Member
[quote}
i have seen grounding conductors split bolted b-4, is it legal or smart for that matter to put several under a split bolt?

h20

[/quote]
Nope. Split bolts are not listed for this use.
John