#97406 02/18/06 08:37 PM
Joined: Mar 2005
Posts: 240
Member
i have a sub 50 amp sub panel that i want to put in a detached maint/gar building.
to save money on wire i am going to run two #6's for the lines and one #8 for the neutral(derating the neut)along with a #10 ground. my question is does this sound code compliant, we derate neutrals for the service feeders and this is going to be a feeder so it seems very complicit to me.

am i on the right page? any codes that i am missing which would forbid this derating?
thanks guys,
h20

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Mar 2005
Posts: 240
Member
oh yea it is a metal building which i will bond the beam structure and will drive two ground rods down at the building too.

Joined: Jan 2004
Posts: 1,507
G
Member
By not knowing what your load is, I can't tell you that you can or can't derate the neutral. Also, I would be interested in how you terminate the neutral and ground wires in the sub panel. Where do you connect the Grounding Electrode Conductor in the sub panel?


George Little
Joined: Jun 2005
Posts: 821
S
Member
There's no need to install ground rods if you run a separate equipment grounding (bonding) conductor (E.G.C.) to the detached garage.

See more about this topic here: https://www.electrical-contractor.net/ubb/Forum1/HTML/006874.html

Joined: Jun 2005
Posts: 821
S
Member

Joined: Dec 2003
Posts: 751
E
Member
Hold on. You must ALWAYS install a grounding electrode system for a detached building with more than a single multiwire branch circuit. It doesn't matter if your have three or four wires; with or without an equipment grounding conductor.
see 250.32


Earl
Joined: Dec 2003
Posts: 751
E
Member
The neutral may only be derated if there is sufficient straight 240 volt loads to warrant it.
see 220.22


Earl
Joined: Apr 2004
Posts: 60
M
Member
If your neutral busses are specifically listed at 75C and you use 75C rated wire, then #8 copper is fine for a 50A feeder because that wire is still rated at 50 amps.


Mark
Kent, WA
Joined: Jun 2005
Posts: 821
S
Member
My bad.

Yes, a grounding electrode MUST be installed on any detached building.

Joined: Aug 2003
Posts: 173
S
Member
Quote
Yes, a grounding electrode MUST be installed on any detached building.
...that is fed with a feeder.
If you only run a circuit no rod is needed.
See: 250.32