Is the code silent on the length of service cable from meter to disconnect?
|
|
|
|
Joined: Jan 2002
Posts: 1,457
Member
|
Yes. There is no length specified.
|
|
|
|
Joined: Jun 2003
Posts: 1,143
Member
|
Usually falls on the AHJ.
|
|
|
|
Joined: Apr 2005
Posts: 73
Member
|
I once had an inspector tell me, as far as code goes, I could wrap SE all the way around the house as long as I maintained proper distance from doors and windows.
|
|
|
|
Joined: Jan 2005
Posts: 316
Member
|
I can run long lengths on the outside of a house but as soon as I enter into the dwelling I must hit the panel/disconnect ASAP. Where I am they only want 3' or less. This is because it's unfused. If the disconnect is outside they want it as close as possible to the meter. Same reason - unfused. I wired an addition a few months ago and had to move the meter - I tried to get the AHJ to let have 7' of SE cable inside the basement. Just enough to reach from new meter location to existing panel. NO go. Had to set an enclosed breaker then re-feed the existing panel with 4 wire and treat it as a sub. separating the grounds and neutrals.
|
|
|
|
Joined: Jan 2003
Posts: 4,391
Moderator
|
This is because it's unfused. If the disconnect is outside they want it as close as possible to the meter. Unless there is a local amendment they can only ask for that they can not enforce it. As has been mentioned you can wrap the house with service entrance conductors before you get to the disconnect.
Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|
|
Joined: Jan 2005
Posts: 316
Member
|
Yes - that may be... But we all know that Sometimes it's easier to do it as they want They all fall back on that sentence in the front of the code book ;subject to the authority having jurisdiction. As I see this it's not they want anything crazy and it does limit the amount of unfused cable. I try and pick my fights now-a-days and this one is not worth the fight. I could fight it and they will hold up releasing the service to the POCO, thus holding up the project. I feel this would be a dis-service to the customer. Just my thoughts on this
|
|
|
|
Joined: Jan 2003
Posts: 1,429
OP
Member
|
Well we just had an inspector, that said it has to be as near as possible, we had 3 ft entering the building, so i guess not all New Jersey inspectors, are not up to speed.
|
|
|