I feel I need to run 2 circuits for the GDOs (3 of them) if a receptacle, or lighting outlet is also supplied. (My own 1/2 HP units draw 5 amps each)
Thoughts?
|
|
|
|
Joined: Jan 2004
Posts: 1,507
Member
|
From a real world prospective, you are not likely to have a problem. It certianly is not a fire or shock hazard but I'm sure if you operated all 3 GDO's at the same time you might trip the breaker. Depending on what else you have on the circuit- air compressor, freezer or other larger appliances, you might trip the breaker when you use only one GDO.
So this guy has a 4 car garage- he/she can afford the additional circuit(s).
George Little
|
|
|
|
Joined: Dec 2003
Posts: 751
Member
|
I have a three car garage, and I ran a single circuit to all three openers. I fully expected to have to run a second circuit for the last of the three openers. But, the circuit held when I opened or closed all three at the same time. (added one opener at a time over several years) I did run a separate circuit for the lights and receptacles. Are you trying to avoid installing a panel in the garage? The NEC makes it clear that if you run a multiwire branch circuit (sharing the same neutral with two hots) to a detached garage, that it constitutes a single circuit, and a panel (and the ground rods) are not required.
Earl
|
|
|
|
Joined: Apr 2005
Posts: 73
Member
|
I also have 3 openers on same circuit. The only time I have tripped a breaker was when I had an elect heater plugged into same circuit I was using table saw and someone else was using skill saw at same time.
It also had no affect on doors because they are on circuit by themselves.
|
|
|
|
Joined: Mar 2001
Posts: 2,056
OP
Member
|
Thanks, guys.
It is an attached garage, and my main concern was NEC compliance regarding the aforementioned article. As far as performance, it is probably a crap shoot. If someone operates all 3, the CB might not handle the starting currents.
BTW,
I ran a 2nd circuit.
|
|
|
|
Joined: Dec 2004
Posts: 1,064
Member
|
ground to the left or ground to the right on the opener receps?
Dnk..
|
|
|
|
Joined: Aug 2005
Posts: 251
Member
|
1 dedicated circuit for the 3 openers sounds perfect.