Lighting outlets and receptacle outlets on the same branch circuit in a non-residential facility. Assuming adequate circuit capacity, is this a code, or design issue?
Thanks.
|
|
|
|
Joined: Jan 2004
Posts: 1,507
Member
|
Design issue.
Prior to the use of EBU's in Michigan we kept the lights and receptacles separate.
George Little
|
|
|
|
Joined: Feb 2005
Posts: 693
Member
|
I believe the same 50% rule applies.
Larry Fine Fine Electric Co. fineelectricco.com
|
|
|
|
Joined: Mar 2001
Posts: 2,056
OP
Member
|
Thanks guys. It must be one of those mysterious "hearsay code" rules.
Larry,
210.23(A)(2) would seem to specifically exclude fixtures from the 50% rule?
|
|
|
|
Joined: Feb 2005
Posts: 693
Member
|
Then you have my blessings. There is still a concern that a malfunctioning equipment could leave one in the dark, but egress lighting should come into play.
Larry Fine Fine Electric Co. fineelectricco.com
|
|
|
|
Joined: Apr 2002
Posts: 7,382 Likes: 7
Member
|
Redsy: Design issue...albeit a questionable design, can't put the NEC to blame. As Larry said, lighting issue may arise.
All in all, NOT on my comm job.
John
John
|
|
|
|
Joined: Feb 2005
Posts: 693
Member
|
To continue the discussion, I rarely combine lighting and receptacles even in residential work. It saves money, time, troubleshooting, and is better for the homeowner, who doesn't lose 100% of power in a room from a single fault.
Larry Fine Fine Electric Co. fineelectricco.com
|
|
|
|
Joined: Jan 2003
Posts: 4,391
Moderator
|
Suppling the 120 volt receptacles from the 277 volt lighting circuits raises heck with PCs and power tools.
Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|
|
Joined: Feb 2005
Posts: 693
Member
|
Yeah, but if you're in a hurry, it's great for a few minutes.
Larry Fine Fine Electric Co. fineelectricco.com
|
|
|
|
Joined: Mar 2001
Posts: 2,056
OP
Member
|
Thanks guys! There were several time in my old facility when miss secretary plugged in a ceramic heater to warm her toes and left others "in the dark". This case invloves pulling a new surface run off an existing flush receptacle, in order to eliminate an extension cord (no additional load expected). But, as it turns out the receptacle is fed from the light switch in the storage room behind it. I'm not yet sure if any other lights(or receptacles)are on the circuit.
|
|
|