Can I feed a sub-panel underground in a commercial building with #2 USE-2 aluminum wire connected to a 100amp breaker, under the 2005 NEC?
shortcircuit
|
|
|
|
Joined: Nov 2000
Posts: 2,148
Member
|
Don(resqcapt19)
|
|
|
|
Joined: Jun 2004
Posts: 613
OP
Member
|
Violation of 110-14(C)(1)a ?
And the 6ft rule is gone in the 2005 NEC...right
shortcircuit
|
|
|
|
Joined: Jan 2004
Posts: 1,507
Member
|
Don- can you elaborate? I agree with part of your answer but the question is not clear if the wiring is outside the building or not.
Also not clear if it's in conduit or not. Edited for added thought.
[This message has been edited by George Little (edited 01-11-2006).]
George Little
|
|
|
|
Joined: Jun 2004
Posts: 613
OP
Member
|
George... the wire will be in pvc and the only part "in" the building is where it emerges from the slab to feed the panel...
shortcircuit
|
|
|
|
Joined: Sep 2003
Posts: 650
Member
|
Umm, how about 310.15 in particular the fact that table 310.16 gives the ampacity of #2AL with 75C insulation and _terminations_ at 90A?
You'd need to jump a couple of hoops to use the 90C column, and 310.15(B)(6) doesn't apply here.
-Jon
|
|
|
|
Joined: Jan 2004
Posts: 1,507
Member
|
The '02 code permits 6 feet of conductor inside the building and the '05 doesn't. That's probaby what Don was getting at and Winnie is right about the ampacity thing. Max overcurrent 90a.
George Little
|
|
|
|
Joined: Jun 2004
Posts: 613
OP
Member
|
Thank you for the feedback...
shortcircuit
|
|
|
|
Joined: Nov 2000
Posts: 2,148
Member
|
My issue is the ampacity of the conductor is 90 amps and cannot be protected by a 100 amp breaker. Don
Don(resqcapt19)
|
|
|
|
Joined: Jan 2005
Posts: 91
Member
|
George,
Just curious about why were you were asking if the conductors were inside or outside of the building. Does this matter?
[This message has been edited by Helectric (edited 01-12-2006).]
|
|
|