ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Safety at heights?
by HotLine1 - 04/23/24 02:17 PM
Old low volt E10 sockets - supplier or alternative
by gfretwell - 04/21/24 11:20 AM
Do we need grounding?
by gfretwell - 04/06/24 08:32 PM
UL 508A SPACING
by tortuga - 03/30/24 07:39 PM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (HotLine1), 210 guests, and 8 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Page 1 of 3 1 2 3
#96858 01/01/06 11:07 AM
Joined: Jan 2003
Posts: 4,391
I
iwire Offline OP
Moderator
Last Month there was a storm on Cape Cod MA, this caused wide spread power outages. As a result we where called in to tie in three 800 KW temporary generators into three separate supermarkets.

Each unit was a very new trailer mounted Caterpillar genset.

While making up the connections we could not help but notice this sticker.

[Linked Image]

Should we have packed up and gone home?

[This message has been edited by iwire (edited 01-01-2006).]


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#96859 01/01/06 12:40 PM
Joined: Feb 2005
Posts: 361
C
Member
It's early...shouldn't the sticker state: At least/minimum 25 ohms to ground?


~~ CELTIC ~~
...-= NJ =-...
#96860 01/01/06 02:09 PM
Joined: Feb 2005
Posts: 219
S
Member
You could have used the building gnd system.

#96861 01/01/06 02:13 PM
Joined: Jan 2003
Posts: 4,391
I
iwire Offline OP
Moderator
Quote
You could have used the building gnd system.

We did. [Linked Image]

However I still have no reason to believe that the buildings grounding electrode system provided less than 25 ohms of resistance.


Bob Badger
Construction & Maintenance Electrician
Massachusetts
#96862 01/01/06 02:18 PM
Joined: Jun 2004
Posts: 220
T
Member
does this have anything to do with it being on a tralier? I would suspect they did mean 25 ohms or less, not at least 25 ohms.

#96863 01/01/06 02:22 PM
Joined: Feb 2005
Posts: 219
S
Member
Normally when Bldg Steel, UFER, Water & Gas are all bonded you will be well below 25 ohms.

[This message has been edited by sierra electrician (edited 01-01-2006).]

#96864 01/01/06 02:34 PM
Joined: Jan 2003
Posts: 4,391
I
iwire Offline OP
Moderator
I would not say you normally assume it will be less than 25 ohms.

That depends entirely on the 'dirt' in the area.


Bob Badger
Construction & Maintenance Electrician
Massachusetts
#96865 01/01/06 02:41 PM
Joined: Jan 2003
Posts: 4,391
I
iwire Offline OP
Moderator
To expand a bit.

What difference does 1, 10, 25 or 100 ohms to ground make anyway?

A fault on the load side of the generators breaker will not use the earth for fault clearing.


Bob Badger
Construction & Maintenance Electrician
Massachusetts
#96866 01/01/06 02:46 PM
Joined: Feb 2005
Posts: 219
S
Member
I would also never assume it. In my experience in my area this is what I have found.
When it is "criticle" to acheive the requested ohms you should always measure it.

#96867 01/01/06 09:35 PM
Joined: Mar 2004
Posts: 391
B
Member
This isn't exactly on topic, but it's related to something I've always wondered:

It seems like everyone talks about earth impedence being less-than or equal-to 25 ohms. That doesn't really make sense to me. How can earth have a definite resistance? Your resistance has to be between two points on a circuit, and assuming the ground rod is A, where is B? And if you increase the distance between the two points aren't you increasing the resistance?

What's going on when people talk about "earth impedence?"

-John

Page 1 of 3 1 2 3

Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5