1 members (Scott35),
182
guests, and
11
robots. |
Key:
Admin,
Global Mod,
Mod
|
|
|
Joined: Aug 2005
Posts: 251
OP
Member
|
We have to bond the hot, cold water and the gas line.
If its a 200amp service do I need to use #4 copper or can I just use #6?
Where in the code is this? Thanks
Shake n Bake
|
|
|
|
Joined: Jan 2003
Posts: 4,391
Moderator
|
First off you really do not have to make any special effort to bond the gas line, that will be done by the EGC of the equipment connected to the gas line.
As far as the sizes take a look at Table 250.66
Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|
|
Joined: Jan 2005
Posts: 5,445 Likes: 3
Cat Servant Member
|
Trick, I think you are confusing "bonding" with "grounding."
This is also an area that is usually modified by your local codes, so you will want to check thing out at city hall, as well.
The wire that goes to your ground rod....the "grounding electrode conductor"....is specified by the NEC to need be no larger than #6, without regard to the size of the service. Many places have raised this to a minimum of #4 solid, and further require it be in pipe for extra protection.
Metal parts of the house that are likely to become energised are required to be "bonded" to the system. Such thing include the water line...but the gas service again is an area that local codes differ about. In any event, the NEC specifies a #10 bonding jumper, but many places specify at least a #8 wire be used.
You are no longer allowed to use the water service as a "ground;" you need that ground rod. You are, howerver, required to "bond" the water line.
|
|
|
|
Joined: Jan 2003
Posts: 4,391
Moderator
|
Reno In any event, the NEC specifies a #10 bonding jumper You are no longer allowed to use the water service as a "ground;" I have no idea what you mean with either of those statements.
Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|
|
Joined: Aug 2005
Posts: 251
OP
Member
|
Well we ground the water line, but in addition..
We have to have a jumper the connects the cold to the hot and then to the gas line.
We ussually do this at the hot water heater. Thats bonding the gas line isn't it?
Shake n Bake
|
|
|
|
Joined: Jun 2004
Posts: 220
Member
|
I would look at 250.104(b). Now as to what circuit rating to use, not as sure. for a 200 amp it says #6, but is that what would energize it?
Reno, could you elaborate on the water pipe grounding. Is that something in the 2005 NEC?
[This message has been edited by trekkie76 (edited 12-21-2005).]
|
|
|
|
Joined: Mar 2003
Posts: 849
Member
|
Water Line Service Grounding Electroide Systems (250.52) Sized per 250.66 (#4) If theres 10 ft. or Metal underground. If not its then its Bonding (See 250.104(A.1))Still sized by 250.66.
Gas piping 250.104B (Other metal Piping) #6 copper . Unless pipe is grounded by an equipment grounding conductor of a circuit thats using the Gas . The equipment grounding conductor is then an effect bond.
|
|
|
|
Joined: May 2003
Posts: 2,876
Member
|
Where I am in what has been refered to as the soveriegn city, of the soveriegn state of SF, CA. Water is required as an electrode and/or bond depending on how you look at it, and if a UFER is involved. Water with no UFER, would be supplimented with rods. With a Ufer, which would be full sized, water would be bonded anyway, in the proccess making it an electrode....
Hot to cold at the water heater...
Gas bond, at the second fitting past the meter - required! They'll even let you use the GEC so long as it is not between the electrode and panel.
Mark Heller "Well - I oughta....." -Jackie Gleason
|
|
|
|
Joined: Jan 2005
Posts: 5,445 Likes: 3
Cat Servant Member
|
Perhaps I should have said you're not allowed to use the water line as your ONLY ground....250.53(D) ays the pipe shall comply with (1) and (2)...and (2) says the pipe shall be supplimented. We often forget that there are type of non-conductive pipe that pre-date plastic. Many cities still have wood water mains...and, more recently, WWII started the use of "orangeburg," a pipe made of asphalt-impregnated cardboard.
As far as the bond wire needing to be !0 or larger, I stand corrected....the NEC calls for it to be at least #8. Formerly, this was a local ammendment- it appears that the NEC has caught up! 250.104 is what I am referring to.
|
|
|
|
Joined: Jan 2003
Posts: 4,391
Moderator
|
To be clear we are required to use a metal water line as an electrode as long as there is 10' of it in direct contact with the earth. It does not matter what is beyond that 10'. An 8' rod is an electrode so it only follows that 10' of metal water line in the ground is an electrode. It will not matter if that 10' of metal line is supplied by non-conductive mains.
In the big picture it may be better if you water line was not electrically continuous with your neighbors.
Yes we must supplement it with one or sometimes two additional electrodes. My guess is that is required as many times people disconnect the GEC from the water line and do not put it back.
I will have to look but I do not believe there is a minimum size bonding conductor for a gas line.
Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|
Posts: 5,445
Joined: January 2005
|
|
|
|