#96675 12/17/05 07:27 PM
Joined: Dec 2002
Posts: 308
E
Edward Offline OP
Member
Does the code require a running board within 7 feet of a crawl space entrance to protect the NM cable?

I thought that section only applied to attic space.

Thanks
Edward


Thanks
Edward
Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#96676 12/17/05 07:51 PM
Joined: Jun 2004
Posts: 220
T
Member
334-15c doesnt say anything about the enterance to the basement, just that if you run against the joists, it must be in a bored hole, or on a running board.

#96677 12/18/05 10:25 PM
Joined: Mar 2005
Posts: 1,213
S
Member
What exactly is a "running board"? NEC doesn't define it, and Webster only uses that word in reference to trucks...

#96678 12/19/05 02:45 AM
Joined: Jul 2004
Posts: 9,923
Likes: 32
G
Member
There are several examples of running boards in the handbook


Greg Fretwell
#96679 12/19/05 10:31 AM
Joined: Dec 2002
Posts: 308
E
Edward Offline OP
Member
I understand if it is a finished basement. As 334-15 (C) requires and as 334-23 to 320-23 in attic spaces.

But my question is about crawl spaces.
What do you think? Is a guard strip or a running board required?

Thanks
Edward


Thanks
Edward
#96680 12/19/05 06:10 PM
Joined: Jun 2004
Posts: 220
T
Member
I guess you have to describe to me what you call a crawl space then. If it is under a house, I call it a basement even if I have to crawl on hand and knee.

I would still say you need a running board, or bored holes.

Steve, a running board is a board run perpendicular to the joists and wires(smaller that 2#6 or 3 #8) are stapled to it.

#96681 12/19/05 07:06 PM
Joined: Dec 2005
Posts: 64
J
Member
334.15(C) says unfinished basements. so we have to define a basement.

there is a mention to crawl spaces under requirements for gfci. 210.8 (A) (4)
so the code does recognize a difference.

haveing spent a few days in a crawlspace, i say it is very different from a basement.

#96682 12/19/05 07:51 PM
Joined: Dec 2002
Posts: 308
E
Edward Offline OP
Member
I describe a crawl space where you crawl on your stomach most of the time and rarely on your knees and hands.

A basement is where you can walk around.

Edward
Thanks


Thanks
Edward
#96683 12/19/05 11:01 PM
Joined: Feb 2003
Posts: 288
Y
Member
If you have to spend any time worrying about whether or not you are about to lay your head down on an animal carcass, you are in a crawl space. I've never had that feeling in a basement.

#96684 12/20/05 03:54 AM
Joined: May 2003
Posts: 2,876
E
e57 Offline
Member
"I've never had that feeling in a basement."

I think that soley depends on the cleanliness of the basement in question...

Anyway, reguardless of basement, attic or crawl space, it is accessible, and exposed work, even if the client is not going to go in there... 334.15(A) says follow the surface of framing or running boards... (B)"shall be protected from physical damage where necessary..." So IMO, if it is an accessable basement, attic or crawl space, and you would know of it being accessable, seeing that you are in it, it could be subject to damage, or become a hazard for the next guy down the line. I think 334.15(B)+(C) would apply... If it is accessible it is exposed work...

In an attic type crawl space 320.23 would apply... As 334.23 would direct you there for "accessible attics or roof spaces"


So where is this "Crawl Space", above below or through the building?


Mark Heller