JBD A single throw inverted design where the fuses and the switch blades are "above" the line contacts. Bolted pressure type switch blades are allowed to be barriered. Have you ever seen any of these in the field? I have installed and serviced a large number of disconnects and have never seen one designer for bottom feed.
Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|
|
Joined: Jun 2004
Posts: 220
Member
|
I think 404-6(C) discusses this, not line and load per say, but that the breaker terminals to the load must be de energized with the breaker in the open position. That is probably why the line in terminated where it is, by design of the breaker.
|
|
|
|
Joined: May 2002
Posts: 1,716
Member
|
Trekkie, in a feed through breaker the terminals to the load would be deenergized if the other end terminals were fed from the source, this would be regardless of which end terminals were used. Here , here , here , and here are some answers to this from SQ D Roger
|
|
|
|
Joined: Jun 2004
Posts: 220
Member
|
Roger, you are correct. I was looking at the section, and it made sense at the time, but as soon as I read your post I realized I was in error.:O
|
|
|