1 members (Scott35),
528
guests, and
22
robots. |
Key:
Admin,
Global Mod,
Mod
|
|
|
Joined: Jan 2004
Posts: 1,507
OP
Member
|
What good is an 601a. fuse?
Meant to 601a in the Subject line :0
[This message has been edited by George Little (edited 12-05-2005).]
George Little
|
|
|
|
Joined: Jan 2003
Posts: 4,391
Moderator
|
A question I have asked myself more than once.
I hope an answer is presented.
Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|
|
Joined: Jul 2004
Posts: 9,931 Likes: 34
Member
|
The only other reference I see is in 430.52ex2(d) and the necessity of 601a doesn't really make sense.
Greg Fretwell
|
|
|
|
Joined: Jul 2004
Posts: 9,931 Likes: 34
Member
|
Are they really saying I could use a 601a time delay Type L fuse at up to 300% of FLA vs 175% for 600a or less? (when the rest of 430.52 Ex1 & Ex2 is met)
I don't know and I have never seen a 125 HP motor
Greg Fretwell
|
|
|
|
Joined: Sep 2001
Posts: 806
Member
|
AFAIK, the 601A fuse is used when you want to fuse an 800A disconnect at 600A.
Essentially, a 600A fuse in the 800A package.
|
|
|
|
Joined: Jan 2004
Posts: 1,507
OP
Member
|
We have an IAEI Seminar 12/8 & 9 and the Bussman rep is scheduled to be there. I'll bounce it off him and bring back the info.
George Little
|
|
|
|
Joined: Aug 2003
Posts: 1,374
Moderator
|
I have been told that the after 600 amps, the physical size of fuses changes. If you have equipment that willonly accept fuses greater tahn 600 amps, but you want 600 amp protection, you use a 601 amp fuse.
Ryan Jackson, Salt Lake City
|
|
|
|
Joined: Jan 2003
Posts: 4,391
Moderator
|
Ryan that makes sense but why do we not have 101, 201, 401, 801 amp fuses as well for the same reason?
Bob Badger Construction & Maintenance Electrician Massachusetts
|
|
|
|
Joined: Dec 2003
Posts: 751
Member
|
because they make adapters for the smaller sizes?
Earl
|
|
|
|
Joined: Aug 2003
Posts: 1,374
Moderator
|
Ryan Jackson, Salt Lake City
|
|
|
Posts: 1,158
Joined: May 2003
|
|
|
|