#96537 12/08/05 08:51 PM
Joined: Oct 2000
Posts: 4,116
Likes: 4
Member
...from the ECN Archives ... [Linked Image]
(Dan Neeser is from Bussmann)
https://www.electrical-contractor.net/ubb/Forum1/HTML/001080.html

[This message has been edited by Bill Addiss (edited 12-08-2005).]


Bill
Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#96538 12/08/05 08:56 PM
Joined: Apr 2002
Posts: 7,382
Likes: 7
Member
Earlydean:
I had the same thought as you, but thought it out again.

Not having a Bussman Catalog handy, does not a 601 amp fit an 800 amp disco, and the 801 fits the 1200 amp disco I'm familiar with the adaptors for 30-60-100-200 sizes, and never seen anything larger.

'601' is referenced within 240-6 (A) but '801' is not.

Now that I said all of that......still??????

jOHN


John
#96539 12/09/05 08:46 PM
Joined: Jan 2004
Posts: 1,507
G
Member
Here's the deal per the Bussman rep. The contractor could install a 800a. or 1200a. Safety Switch with conductors that were only adequate for 600a. Now if the customer decides to expands his capacity to 800 or 1200 amps all he needs to do is change the conductors and the fuse and not have to change the switch. This is apparently is a significant cost saving measure. From what Bussman is telling me, it's the only "Listed" way of doing this sort of thing. Works for me.


George Little
#96540 12/10/05 12:03 AM
Joined: Jul 2004
Posts: 9,931
Likes: 34
G
Member
I have seen this done with 400a equipment and 225a fuses. It bothered me so much I have a proposal in the 1999 ROP.
CMP10 said nobody would be dumb enough to shove a 300 or 400a fuse in there without upsizing the conductors so it wasn't a problem. I guess they never saw a "maintenance man"/electrician.


Greg Fretwell
#96541 12/10/05 09:12 AM
Joined: Dec 2003
Posts: 751
E
Member
Has CMP 10 never seen pennys in the fusebox? Or copper pipe in the fuse holder? Or even #12 copper wire jammed into the fuse holder or meter socket?


Earl