Joined: Apr 2004
Posts: 60
M
Member
gfretwell wrote: I am still not sure why he couldn't ground the service in one of the disconnects with a #2 and be done with it.

That's exactly what he should do. As long as the neutral is sized equal to or above the 250.66 size, it can ground either or both panels. Just because you are permitted to run GEC taps doesn't mean you have to.

Also, what size service entrance conductors were run on the line side of the meter? Need to make sure that a #2 is large enough by examining all of the SE conductors.


Mark
Kent, WA
Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: Jun 2004
Posts: 613
S
Member
Here is a quote from Soares based on your described installation...

"If the installer chooses to, an individual grounding electrode conductor may be installed from each service disconnecting means enclosure to the grounding electrode.

In this case the GEC is sized for the service-entrance conductor serving that enclosure.

The code does not specifically address or prohibit this concept but it is similar to connecting taps to a common grounding electrode conductor. In this case the taps are connected directly to the electrode."

shortcircuit

Joined: Jan 2004
Posts: 1,507
G
Member
Mark- There are no Service Entrance conductors on the line side of the meter. There is an underground lateral coming from the utility company to the meter and the utility company will not permit the GEC to orginate in their meter. I appreciate the reference to Soares and I guess since we have two service panels we are dealing with coming out of each panel with a properly sized GEC to the electrode system. As Greg indicated a person could use Note #1 of T. 250.66 and then based on the "Tap" rules come out of the other panel with a properly sized tap conductor and save the cost of installing two conductors all the way to the electrode.


George Little
Joined: May 2003
Posts: 2,876
E
e57 Offline
Member
"no Service Entrance conductors on the line side of the meter. There is an underground lateral coming from the utility company"

"underground lateral from the utility company" = "Service Entrance conductors"

And the GEC needs to be sized for them...

Anyway... I think its clear the code wants one GEC per lateral. Although Soares opinion might differ.... (What if one service is removed, and you have a just a #6 covering the grounding for 350MCM SE conductors?)
Quote
(D) Grounding Electrode Conductor Taps. Where a service consists of more than a single enclosure as permitted in 230.40, Exception No. 2, it shall be permitted to connect taps to the grounding electrode conductor.(singular) Each such tap conductor shall extend to the inside of each such enclosure. The grounding electrode conductor[i](singular) shall be sized in accordance with 250.66, but the tap conductors shall be permitted to be sized in accordance with the grounding electrode conductors[i](plural) specified in 250.66 for the largest conductor serving the respective enclosures. The tap conductors shall be connected to the grounding electrode conductor.[i](singular) in such a manner that the grounding electrode conductor.[i](singular) remains without a splice.

Commentary from 230.40 exception 2... "Note that in such cases the lateral conductors are considered [i]one service lateral."

Also, how can anyone do a complete job without knowing what the meter is fed with, (Not opening the meter) otherwise you would never know what size the GEC should be.

IMO the GEC crimps or welds should be right below the equipment. Or run a single conductor in and out of both panels. The allowing of taps seems to be making it easier for you... "the tap method eliminates the difficulties found in looping grounding electrode conductors from one enclosure to another." (From the commentary following 250.64(D) )


Mark Heller
"Well - I oughta....." -Jackie Gleason
Joined: Jan 2004
Posts: 1,507
G
Member
I think someone should read in Article 100 about the definition of "Service Entrance Conductors" - They are Not the lateral. And if your going to copy and paste from the NEC you might want to check the copyright permissions.


George Little
Joined: Oct 2004
Posts: 806
Member
George:

Please look at this:
https://www.electrical-contractor.net/ubb/Forum1/HTML/006592.html

That should ally your concerns over quoting Code in the forums. [Linked Image]


Stupid should be painful.
Joined: Jan 2004
Posts: 1,507
G
Member
Thanks for the link and information on copy and paste. I was and still am not real comfortable with copying and pasteing but I feel better now and that's what this forum is all about. That said, I found some very enlightening information in Soares Grounding that covers the subject of this thread. Check out p.118 of Soares Grounding 8th edition. It appears that coming out of muliple Service panel and running to the Grounding Electrode with a GEC is one of many ways of complying with the NEC.


George Little
Joined: Jul 2005
Posts: 56
P
Member
What I am curious about is whether the lugs in the meter enclosure are UL listed for more than one conductor???

Joined: May 2003
Posts: 2,876
E
e57 Offline
Member
George, "Service Entrance Conductors" can be pretty broad. (Depending on where you are...) Here, where I am, it is entrance to, or attachment to the building. Most service equipment and metering (customer owned) are inside...
Quote
Service conductors is a broad term and may include service drops, service laterals, and service-entrance conductors. But this term specifically excludes any wiring on the supply side (serving utility side) of the service point.
In terms of the definitions from the NEC, take a look at "Service Lateral", and "Service Point", both help determine where "Service Entrance Conductors" begin.

Anyway, my point was that what you have is two GEC's, and two connections to the water are a splice in what is supposed to be one conductor. (If you are inspecting to the NEC, not Soares...)


Mark Heller
"Well - I oughta....." -Jackie Gleason
Joined: Mar 2001
Posts: 345
T
Member
Quote
Anyway, my point was that what you have is two GECs, and two connections to the water are a splice in what is supposed to be one conductor. (If you are inspecting to the NEC, not Soares...)
The code specifically permits the GEC to run from one electrode to another.
Quote
250.64 Grounding Electrode Conductor Installation.
Grounding electrode conductors shall be installed as specified in 250.64(A) through (F).
(F) To Electrode(s). A grounding electrode conductor shall be permitted to be run to any convenient grounding electrode available in the grounding electrode system or to one or more grounding electrode(s) individually. The grounding electrode conductor shall be sized for the largest grounding electrode conductor required among all the electrodes connected to it.
I cannot see how two GECs that are terminated on the same electrode would be a spliced GEC violation just because they both originated in the same vicinity. By that logic the separate service permitted for fire pumps could not be grounded to the electrodes that are used for the main service. In fact any failure to use the same electrodes for a separate service would be a violation of
Quote
250.58 Common Grounding Electrode.
Where an ac system is connected to a grounding electrode in or at a building as specified in 250.24 and 250.32, the same electrode shall be used to ground conductor enclosures and equipment in or on that building. Where separate services supply a building and are required to be connected to a grounding electrode, the same grounding electrode shall be used.
Two or more grounding electrodes that are effectively bonded together shall be considered as a single grounding electrode system in this sense.
--
Tom Horne

"This alternating current stuff is just a fad. It is much too dangerous for general use." Thomas Alva Edison


Tom Horne

"This alternating current stuff is just a fad. It is much too dangerous for general use" Thomas Alva Edison