ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
UL 508A SPACING
by ale348 - 03/29/24 01:09 AM
Increasing demand factors in residential
by tortuga - 03/28/24 05:57 PM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
Do we need grounding?
by NORCAL - 03/19/24 05:11 PM
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (ale348), 302 guests, and 14 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
Joined: Apr 2001
Posts: 41
S
smokey Offline OP
Member
I AM INSTALLING THE ELECTRICAL POWER FOR AN INDOOR SPA AND I WAS WONDERING IF ANYTHING IN THE CODE REQUIRES ME TO INSTALL A RECEPTACLE FOR MAINTENANCE PURPOSES ???? PLEASE ANSWER AND STATE CODE REFERENCE

Joined: Oct 2000
Posts: 5,392
S
Member
680-41(a)


Link Copied to Clipboard
Powered by UBB.threads™ PHP Forum Software 7.7.5