by ale348 - 03/29/24 01:09 AM
by NORCAL - 03/19/24 05:11 PM
#95912 10/22/05 05:48 PM
K
Kelley Offline OP
Have you guys run into issue with co detectors being required when there is a direct vented gas or oil appliance i.e. fireplace or boiler etc.
I just ran into this the other day when the inspector came thru for a rough inspection on a new house he brought it up to me. Though he said it was not in our code but the plumbing code. Does anyone have any info or code refs on this. Thanks.
I'm in Massachusetts.
Kelley
#95913 10/22/05 07:13 PM
Here in NJ CO detectors have ben mandatory for a while.
Building with fuel burning appliance, or attached garage.
Hard wired, or battery are OK
Enforced by the Fire Sub-Code Official
#95914 10/22/05 10:35 PM
Where I am (on Long Island, NY) they are required too, and must have some specific Features.
I don't have the actual wording available, but (from memory?) they must be hard-wired (120v) and have a digital display that shows accumulated exposure to CO.
#95915 10/23/05 01:22 AM
are these smoke/co combo or just co detectors? if smoke/combo rough inspection how would the inspector know?
here in wa there is no requirement for co detectors but have to agree that it is a good idea or mandatory canary ownership.
h20
#95916 10/23/05 09:54 AM
Ron Offline
Ron
#95917 10/23/05 02:52 PM
Ron,
Interesting, thanks for the info. That is a bit different than the information we've been given about these things. My info may be dated, (or wrong) but we were told CO Detectors had to be hard-wired in new construction, and some towns even required that special affidavits had to be filed when these were installed.
#95918 10/26/05 08:56 PM
Kelly, I too have been told of this new revision to NFPA-54 Chapter 10 (10.8.3)
It has been in effect since the end of July, I've been told.
It pertains to direct vent appliances, mechanical-vent heating appliances or domestic hot water equipment , where the bottom of the vent terminal is installed below four feet above grade.
There is more to the amendment and I did a search but came up with nothing?
I'll try to get more info tomorrow...
Also there is Nicole's Law under the making which will require a CO detector in all public housing units by Jan 1st 2007.
In memory of Nicole Garofalo, who died in her Plymouth home this past winter when a snow drift blocked the vent for the furnace...
shortcircuit
#95919 10/26/05 10:54 PM
GTE Offline
Bill,
Suffolk County requires hard wired in new Construction.
#95920 10/27/05 12:20 AM
GTE,
I know the Inspectors ask for it, but I'm now wondering where that comes from and if it's a legitimate requirement. The NYS Law Ron linked to says that Cord and Plug, or Battery-Operated units are allowed:
Power source. Carbon monoxide alarms are permitted to be permanently connected to the building wiring system, connected by cord or plug to the wiring system, or battery operated....
#95921 10/27/05 07:14 AM
Ron Offline
Shortcircuit,
Here's the text from 10.8.3
NFPA 54 National Fuel Gas Code 2006 Edition
10.8.3 Installation.
10.8.3.1 Non-recirculating direct gas-fired industrial air heaters shall be installed in accordance with the manufacturer’s instructions.
10.8.3.2 Non-recirculating direct gas-fired industrial air heaters shall be installed only in industrial or commercial occupancies.
10.8.3.3 Non-recirculating direct gas-fired industrial air heaters shall be permitted to provide fresh air ventilation.
10.8.3.4 Non-recirculating direct gas-fired industrial air heaters shall be provided with access for removal of burners; replacement of motors, controls, filters and other working parts; and for adjustment and lubrication of parts requiring maintenance.
I don't see any reference to carbon monoxide detection in the document.
Ron