#95897 10/18/05 02:33 PM
Can somene help me with locating the Section number in the '02 NEC that says that an optional Ground Rod at a light pole for instance, does not need to meet the <25 ohms called for like it is for a System Grounding Electrode? I know it's there somewhere but I can't find it.
George Little
Stay up to Code with the Latest NEC:
>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep
>> 2020 NEC & Related Reference & Study Guides
#95898 10/18/05 04:27 PM
250.54 Supplementary Grounding Electrodes.
Supplementary grounding electrodes shall be permitted to be connected to the equipment grounding conductors specified in 250.118 and shall not be required to comply with the electrode bonding requirements of 250.50 or 250.53(C) or the resistance requirements of 250.56, but the earth shall not be used as the sole equipment grounding conductor.
Don
Don(resqcapt19)
#95899 10/18/05 04:49 PM
Thanks Don. I thought I was losing it because I couldn't find that code reference.
George Little