228
Does anyone have any information on the use of reducing washers?
George Little
UL White Book OUTLET BUSHINGS AND FITTINGS (QCRV) GROUNDING Metal reducing washers are considered suitable for grounding for use in circuits over and under 250 V and where installed in accordance with ANSI/NFPA 70, ‘‘National Electrical Code.’’ That's all I have except they make big holes small.
Thanks Bob- That's what I needed.
George Little
That information really makes me question the technical expertise of UL. Don
Don I think the problem is the difference between test conditions and real life.
I have no doubt you or I could make reducing washers carry fault current if we used a wire brush to remove all paint from the enclosure and tightened the lock nuts decently.
However I know I see reducing washers all the time that are up against paint and loose.
I think an inspector could cite 250.12 Clean Surfaces almost every time.
Personally I dislike everything about reducing washers.
I discussed this matter with the UL representative of CMP 5 (Article 250). He was surprised as well, but looking at the listing standard, it appears as though under test conditions reducing washers that are listed are capable of carrying a tremendous amount of fault current. I don't recall the exat test now, but it was several thousand amps for a substantial duration.
Ryan Jackson, Salt Lake City
I'm sorry, but if the test conditions do not represent a real world installation, the results are worthless. Don
Posts: 9,931 Likes: 34
I vote with Bob. Reducing washers keep the connector from falling out but I would use a bonding nut if I wanted to make a secure grounding connection.
Reducers -- gotta hate 'em....
Every time I see them it's a hack job.
I particularly dislike reducers used at NEMA3R disconnects where the installer is shrinking back from a 1 inch KO goof.
Tesla
I hate RE plates. I would rather screw a plate in the can and make sure there is a ground wire. I have had inspectors fail an installation; he wanted reducing washers; I had bolted a cover plate to the top of the box and had a grounding bushing and ground wire in the EMT. My way was better and I proved it to him with a megger. He made me change it to pass inspection. Still scratching my head Rod.
