ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Increasing demand factors in residential
by gfretwell - 03/28/24 12:43 AM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
Do we need grounding?
by NORCAL - 03/19/24 05:11 PM
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
Cordless Tools: The Obvious Question
by renosteinke - 03/14/24 08:05 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
0 members (), 260 guests, and 20 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#95505 09/16/05 11:30 PM
Joined: Jan 2004
Posts: 1,507
G
Member
Looking at 410.10 I conclude that the canopy of a luminaire is only suitable for luminaire wires and there connecting devices. How much branch circuit conductor is permitted in the canopy?


George Little
Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#95506 09/17/05 07:34 AM
Joined: Sep 2005
Posts: 106
J
Member
George I would say that if the canopy is not marked with a cu. in. capacity then none.
[Linked Image]


Mike
#95507 09/17/05 12:20 PM
Joined: Jan 2005
Posts: 5,445
Likes: 2
Cat Servant
Member
We are required to make all our connections in a "junction box." The fixture canopy, or base, is considered as a "box" when installed.
As such, it is required to have enough space for the usual 6" of 'free conductors." (300.14)

What is not clear is whether there is required to be enough room for a second set of wires to exit, and continue on to the next fixture. It's not even clear if there is required to be room for the switch legs.

A classic example is the "pancake" box....it has room only for wires serving the device; there is no room for these other 'associated' wires.

Personally, I consider it no longer accepted practice to mount a fixture without using a box. Apart from wiring space, the box probides a much better mounting. But I wander....:-)

#95508 09/17/05 01:02 PM
Joined: May 2005
Posts: 706
T
Member
Article 410.10 is as clear as mud to the issue of your post IMO. It seems to say that, but doesn't really say anything about circuit conductors. The only issue I read in it is...

"shall provide adequate space"

...I don'r read this as limiting at all to other conductors that may occupy the space of the canopy. I'd look for the word ONLY for the meaning you're implying.

Dave

#95509 09/17/05 01:06 PM
Joined: Jul 2004
Posts: 9,923
Likes: 32
G
Member
I guess this boils down to the old question, if you terminate 3 #12s in a 6 cu/in pancake can you borrow .75" from the canopy?
Add a .0625" thick ring? (About the thickness of the box material)
... absurd...
If you have 5 wires in there (2H 2N and the grounds) I would have a problem in a pancake, fat canopy or not.


Greg Fretwell