#95495 09/16/05 09:45 PM
Joined: Dec 2002
Posts: 308
E
Edward Offline OP
Member
I finished a fourplex four meter pack with four disconnects on one enclosure.And i have four 60Amp feed through one conduit to each subpanel that are installed side by side in a 36"x48" enclosure. I have pulled only one #10 EGC that is being daisy chained from one panel to the next.
I have a feeling that i need four #10EGC.
Am I correct?

Please show NEC reference because i can not find it.

Thank you
Edward


Thanks
Edward
Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#95496 09/16/05 10:28 PM
Joined: Mar 2005
Posts: 240
Member
And i have four 60Amp feed through one conduit to each subpanel that are installed side by side in a 36"x48"

what kind of raceway?

h20

#95497 09/16/05 10:59 PM
Joined: Dec 2002
Posts: 308
E
Edward Offline OP
Member
One EMT conduit with four "C" conduilets that feed each panel separately. It is not a through feed installation.
I will try to submit picture.

Thanks
Edward


Thanks
Edward
#95498 09/16/05 11:07 PM
Joined: Feb 2005
Posts: 693
L
Member
Ed, the EMT itself should qualify as the EGC for each panel. Otherwise, yes, each feeder should have its own EGC, I believe.


Larry Fine
Fine Electric Co.
fineelectricco.com
#95499 09/17/05 06:47 AM
Joined: Jan 2003
Posts: 4,391
I
Moderator
One EGC for all the circuits is OK.

Quote
250.122(C) Multiple Circuits. Where a single equipment grounding conductor is run with multiple circuits in the same raceway or cable, it shall be sized for the largest overcurrent device protecting conductors in the raceway or cable.

Not sure the power company will be happy with the feeders from 4 different meters to all be in the same conduit.



[This message has been edited by iwire (edited 09-17-2005).]


Bob Badger
Construction & Maintenance Electrician
Massachusetts
#95500 09/17/05 07:33 AM
Joined: May 2005
Posts: 247
T
Member
I don't know why the power company would care, since the feeders are all downstream of the main OCP. The AHJ might care, but I don't see any real issues with it.

#95501 09/17/05 07:43 AM
Joined: Jan 2003
Posts: 4,391
I
Moderator
Power theft would be the power company's issue.


Bob Badger
Construction & Maintenance Electrician
Massachusetts
#95502 09/17/05 12:28 PM
Joined: Jan 2005
Posts: 5,445
Likes: 2
Cat Servant
Member
I think 250.24(C) is the section we want.

As I read it, you are only required to have on GEC (wire to a ground rod). The utility neutral, however, must be bonded to the case of each of the disconects- so the egc will terminate to the neutral buss at each disconnect as well.

#95503 09/17/05 12:33 PM
Joined: Jan 2003
Posts: 4,391
I
Moderator
Reno I believe the GEC would be at the meter stacks with the service disconnect(s) the wires in the EMT are feeders not service conductors. [Linked Image]


Bob Badger
Construction & Maintenance Electrician
Massachusetts
#95504 09/17/05 07:12 PM
Joined: Jan 2005
Posts: 5,445
Likes: 2
Cat Servant
Member
I agree, Iwire.....I only brought up the GEC as this is the sort of application where things get confused easily. After all, there is the question of what to do with the EGC once it reaches the panel.


Link Copied to Clipboard