Has anyone on this forum had any experience with the floor heating system manufacturered by "Heatizon"? Since seeing it on a job installed in a bathroom, I am concerned about the requirement for GFCI protection. The voltage is about 36v. and the primary voltage is 240v. Look at 224.44(G).
George Little
Stay up to Code with the Latest NEC:
>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides
Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep
>> 2020 NEC & Related Reference & Study Guides
#94894 08/18/05 04:28 AM
e57 Offline
I have heard some are adding built-in GFI protection, not sure about this one.... Haven't seen it yet.
And yep, if in a situation described by the code you refferance, requires protection, one way or the other.
#94895 08/18/05 11:48 PM
I left this one alone because we don't do a lot of heated floor in S. Florida.
Reading 424.44(G) I don't see any relief from the GFCI rule because it is 36v.
I would certainly defer to an AHJ who had actually seen one tho.
#94896 08/19/05 12:01 AM
I don’t know anything about the Heatizon system but the digital thermostats included with all the floor systems I have worked with have integral GFCI protection.