ShockMe77, you have shocked me.
I think article 110.3 applies here.
I think that is a major stretch.
110.3 Examination, Identification, Installation, and Use of Equipment.
(A) Examination. In judging equipment, considerations such as the following shall be evaluated:
(7) Classification by type, size, voltage, current capacity, and specific use
Notice it says
"considerations such as" Most reasonable people IMO would consider a 200 amp panel to be safe fed with a 90 amp breaker.
Would you require a 200 amp disconnect feeding a 125 amp load to be fed at 200 amps?
Bob