Joined: Apr 2002
Posts: 558
C
Member
I agree with John. It is perfectly acceptable to use a panel with that has a buss rating higher than the feeder. One thing to be careful about is the lug rating of 200 amp loadcenters since the minimum wire size for many of them is #1. I believe the lugs on 200 and 225 amp Square D loadcenters are rated down to #6.

Curt


[This message has been edited by caselec (edited 08-06-2005).]


Curt Swartz
Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

Joined: May 2005
Posts: 706
T
Member
BobH, I don't know if you're asking about the 200-amp main, or the 200-amp minimum service. I've done the setup that Steve describes, and consider it an additional disconnect. Personally I LIKE having an additional disconnect within sight in that situation.

The 200-amp minimum isn't an NEC requirement, but a local amendment. One town will allow 100-amp if you provide load calculations. I prefer to go with the 200-amp service than to do calculations. It's more time involved to make less money and I'd look like a fool if the additional service were needed in the future.

Dave

Joined: Jan 2003
Posts: 4,391
I
Moderator
ShockMe77, you have shocked me. [Linked Image]

Quote
I think article 110.3 applies here.

I think that is a major stretch.

Quote
110.3 Examination, Identification, Installation, and Use of Equipment.

(A) Examination. In judging equipment, considerations such as the following shall be evaluated:

(7) Classification by type, size, voltage, current capacity, and specific use

Notice it says "considerations such as"

Most reasonable people IMO would consider a 200 amp panel to be safe fed with a 90 amp breaker.


Would you require a 200 amp disconnect feeding a 125 amp load to be fed at 200 amps?

Bob


Bob Badger
Construction & Maintenance Electrician
Massachusetts
Joined: May 2005
Posts: 706
T
Member
A similar situation IMO is running a 60-amp AC disconnect at 30-amps.

Dave

Joined: Jan 2005
Posts: 22
X
Member
ever thought of just useing a main-lug 200A?