220
12
Posts: 9,928 Likes: 34
The only problem with that analysis is a second building with no bonded metalic paths can become another virtual "main" in respect to bonding the neutral.
There is certainly a lot to consider over this issue.
Looking at the case of a detached garage fed via 3-wire cable with bonded neutral and ground, is it really much different than two houses fed from the same transformer, each with a bond a the main service?
In fact if the two homes are fed via metallic water pipes from a common system, it could be considered worse, since with metallic pipes to the detached garage you would need the isolated 4-wire feeder.
Paul, you are correct, but this is outside of the NEC. (POCO's are under the NESC)
I guess the NEC is trying to keep this potential problem at bay on their side.
Roger
Pun intended, Roger?
As a related issue, have you actually looked at the unbalanced current going into the ground from a pole pig? I get about 4a on the one in front of my house measuring the 8ga solid coming down the pole. My GEC is contributing a couple amps of that.
Paul, actually as much as I want to say yes, I didn't think about it to after I hit the "Submitt Reply" button. Roger
Originally posted by gfretwell:
I was the last guy I ever saw using copper and people told me I was screwing up. That's 'cuz you're not supposed to use copper for conduit!
Aw, c'mon now..... You can use it for both surely? After you've pulled wires through there's still plenty of room in the pipe for the water to flow.......
I would love to find a source of appropriately rated RMC in _brass_, with associated fittings. Not for any current job, but because I have an image of polished brass pipe used for an elegant exposed installation.
-Jon
Greg,
One house that had problem with pin hole leaks had a problem with the grounding of the house. A plumber friend of mine called me up and told me that one house kept having pin hole leaks. I said, I am an electrician not a plumber. He said, he was running out of ideas and maybe I could come up with something. Long story short, all I could find was a plastic water filter in the middle of the house. It broke the copper water pipe and didn't have a jumper over it. I ask the plumber where the leaks were, front of house or back, he said back only. Put a jumper across the filter and never had a leak since.
