Section 210.70 requires lighting outlets wall switched for habitable rooms, etc. There is an exception for switched receptacles.
The definition of a lighting outlet is an outlet INTENDED for the installation of a lampholder etc.
On final inspection the contractor put blank covers on the lighting outlets and claimed that the owner would select fixtures (luminaires) at some future date.
Should the inspector accept or reject ?
We are curious in Indiana, because it is a real situation.
Should the word intended be removed from the definition (Article 100) of lighting outlet,therefore requiring a lampholder, luminaire, pendant etc. ?
Alan-- Inspector.
Alan--
I would require at least a keyless; elsewise, the requirements are not met. Without a luminaire, there is no light.
Larry Fine
Fine Electric Co.
fineelectricco.com
Accept it. We as AHJ's can't save the world.
I mean honestly, what do you gain from having them put in a cheesy keyless?
Ryan Jackson,
Salt Lake City
Or a $5.99 Orange Box single bulb & fluted glass fixture from China.
The advantage of keyless over a blank is a functioning light. Why the NEC has the requirement, I don't know specifically if it is for protetion from fire from what some clever people might do to get light, or if it to minumize the hazards of fumbling through a dark room. But for whatever the reason for the code, there is exposure to the hazard until the lights get picked out, ordered, delivered, and installed, which could be a long time. Mix some small kids in and who knows. Are ther bigger things in life to worry about, sure, but I don't think it is unreasonable to require a keyless. As an installer, I wouldn't leave a house for final with just blanks.
Alan:
Leaving that outlet with a blank cover is an accident waiting to happen!
I have called for the installation of at least a lampholder before signing off a final during my career.
REJECT!
You answered your own question.
The NEC requires a lighting outlet, that is all.
If the room uses a switched outlet would you require them to install a floor lamp before you signed off?
It is the same concept.
To me the NEC is crystal clear here, a lighting outlet is not a luminaire.
For those that say reject, please provide the code reference you would cite?
Bob
110.3(A)(8) and the approved plans and specifications!
Switched lighting are required, especially in bathrooms and kitchens!
Common sense, too!
110.3(A)(8)
110.3(A)(8) does not allow an inspector to require items not required by the text of the NEC.
We have built many condos that simply show lighting outlets without Luminaires. The Luminaires will be chosen by whoever buys the condo which may be long after the occupancy permit is released for the building.
No, lighting is not required by the NEC, lighting outlets are required in these locations by the NEC
Common sense, too!
Well that may be true, [Linked Image] but it is no way enforceable by an electrical inspector who works within the rules.
I would still like to hear why it is unsafe to leave a blanked up lighting outlet in a living room but it is perfectly safe to leave a switched outlet without a lamp in the same room.
It makes no sense whatsoever. [Linked Image]
Bob
I am with Bob on this. Perfectly clear to me as well. Joe you as a code guru who has been know to argue the literal wording of the code should certainly be able to see this. You yourself call the blanked up box an outlet. NEC requirement is met. Pass the job according to the code not personal opinion.
[This message has been edited by Electricmanscott (edited 07-30-2005).]