ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals
ECN Shout Chat
ShoutChat
Recent Posts
Increasing demand factors in residential
by gfretwell - 03/28/24 12:43 AM
Portable generator question
by Steve Miller - 03/19/24 08:50 PM
Do we need grounding?
by NORCAL - 03/19/24 05:11 PM
240V only in a home and NEC?
by dsk - 03/19/24 06:33 AM
Cordless Tools: The Obvious Question
by renosteinke - 03/14/24 08:05 PM
New in the Gallery:
This is a new one
This is a new one
by timmp, September 24
Few pics I found
Few pics I found
by timmp, August 15
Who's Online Now
1 members (Scott35), 284 guests, and 12 robots.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate Thread
#94335 07/27/05 10:34 PM
Joined: Mar 2005
Posts: 240
Member
i have never done it but can one splice in an lb it is a conduit body and think it has sufficient cube space although if it is cast suppose grounding would be an issue since there isnt a threaded hole.
anyway just wondering?

Stay up to Code with the Latest NEC:


>> 2023 NEC & Related Reference & Exam Prep
2023 NEC & Related Reference & Study Guides

Pass Your Exam the FIRST TIME with the Latest NEC & Exam Prep

>> 2020 NEC & Related Reference & Study Guides
 

#94336 07/27/05 11:26 PM
Joined: Jul 2002
Posts: 717
M
Member
There are some lb's that are listed to have splices in them provided that the cross sectional area of the splices does not exceed, ah what? I don't have my codebook handy - 40 per cent of the total volume of the fitting?

#94337 07/28/05 01:08 AM
Joined: Jun 2003
Posts: 1,143
D
Member
Courtesy of the '96 Code:
Quote
370-16 (c) Conduit Bodies.
<snip>
Conduit bodies shall not contain splices, taps, or devices unless they are durably and legibly marked by the manufacturer with their cubic inch capacity. The maximum number of conductors shall be calculated using the same procedure for similar conductors in other than standard boxes.

#94338 07/28/05 05:00 AM
Joined: May 2004
Posts: 116
S
Member
watersparkfalls -

From the 2002 NEC Handbook:

314.5 Short-Radius Conduit Bodies.

Conduit bodies such as capped elbows and service-entrance elbows that enclose conductors 6 AWG or smaller, and are only intended to enable the installation of the raceway and the contained conductors, shall not contain splices, taps, or devices and shall be of sufficient size to provide free space for all conductors enclosed in the conduit body.

Short radius conduit bodies are not permitted to contain splices.

And there is also:

314.16(C)

(C) Conduit Bodies.
(1) General. Conduit bodies enclosing 6 AWG conductors or smaller, other than short-radius conduit bodies as described in 314.5, shall have a cross-sectional area not less than twice the cross-sectional area of the largest conduit or tubing to which it is attached. The maximum number of conductors permitted shall be the maximum number permitted by Table 1 of Chapter 9 for the conduit or tubing to which it is attached.
(2) With Splices, Taps, or Devices. Only those conduit bodies that are durably and legibly marked by the manufacturer with their volume shall be permitted to contain splices, taps, or devices. The maximum number of conductors shall be computed in accordance with 314.16(B). Conduit bodies shall be supported in a rigid and secure manner.
As illustrated in Exhibit 314.4, conduit bodies other than the short-radius type are permitted to contain splices or taps, provided the conduit bodies are marked with their cubic inch capacity. Such conduit bodies are required to have a cross-sectional area not less than twice that of the conduit to which they are attached and are not permitted to contain more conductors than the attached raceway. The volume requirements for splicing or tapping are provided in 314.16(C).
Conduit bodies must be rigidly supported. See 314.23(D)(2) and the exception to 314.23(E), and Exception No. 1 of 314.23(F), which permit the raceway to support the conduit body, provided the conduit body is not larger than the attached raceway.
See 314.28 for requirements that apply to conduit bodies used as pull and junction boxes.

Exhibit 314.4 An example of splices in a raceway-supported conduit body.


Hope this helps.

Steve


Thanks
Steve
#94339 07/28/05 11:11 AM
Joined: Mar 2005
Posts: 240
Member
thanks guys that helps ALOT!
h2o

#94340 07/29/05 11:19 PM
Joined: Jun 2003
Posts: 1,143
D
Member
All hail the Handbook!
(I love that thing)

Good call, Steve.



[This message has been edited by DougW (edited 07-29-2005).]